All Singing All Dancing E.V. Charger.

Is this a good one?

https://www.bing.com/videos/search?q=Youtube+Artisan+electrician+EV+charger+install+Zappi+home&docid=608055082115925091&mid=AC8C58AA73CB9E199546AC8C58AA73CB9E199546&view=detail&FORM=VIRE


Z.
  • Well we may not see so much kit with things like  these detectors inside then - pity really as having all the safety stuff in one place is much cleaner than several ADS type items all of which need different  testing.


    M.


  • Former Community Member
    0 Former Community Member
    Just out of interest; the regs state do they not that the designer/installer (that's us) is liable for the correct operation of the kit... Zappi or matt:e or whomever are presumably not liable if their kit fails and kills someone in the case of an open neutral or similar? It's us who are liable. (So I was told by NAPIT...). So better to stick with earth rods and RCDs as known (and testable) technology, even if it's a pain to dig an earth rod hole? Just wondering what you old hands think? :)
  • Just out of interest; the regs state do they not that the designer/installer (that's us) is liable for the correct operation of the kit... Zappi or matt:e or whomever are presumably not liable if their kit fails and kills someone in the case of an open neutral or similar? It's us who are liable. (So I was told by NAPIT...).

    Eh? Which regulation is that? It doesn't seem reasonable that we should be liable for things we're not in control of (the internals of manufactured equipment).

       - Andy.
  • Andy


    I think Mr Fox and NAPIT are referring Note 5 to Regulation 722.411.4.1. As these novel O PEN type devices have no BS or BS EN or harmonised standard they have to be designed in and installed as a Departure in accordance with 133.1.3 and 511.1 and 511.2.


    JP
  • John Peckham:

    Andy


    I think Mr Fox and NAPIT are referring Note 5 to Regulation 722.411.4.1. As these novel O PEN type devices have no BS or BS EN or harmonised standard they have to be designed in and installed as a Departure in accordance with 133.1.3 and 511.1 and 511.2.


    JP


    Ah, reassuring it's not thought to be a general requirement.


    The note reads:



    NOTE 5: See Section 511. BS 7671 does not deal with the safety requirements for the construction of electrical equipment. Where equipment to be used is not covered by a British or Harmonized Standard or is to be used outside the scope of its standard, it is the responsibility of the electrical installation designer or other person responsible for specifying the installation to establish that the manufacturer of the equipment has ensured that the equipment satisfies the safety objectives of the relevant Directive(s), as it will not benefit from a presumption of conformity afforded by the appropriate product standard.

    my interpretation is that our responsibility would be merely to enquire of the manufacturer whether it meets the appropriate levels of safety - we'd still not be liable if the kit later failed.


        - Andy.
  • Yes Andy as the Note says, "it is the responsibility". So the designer or the specifier needs to demonstrate due diligence in the selection of the device. I think that obtaining a Declaration of Conformance listing compliance with all the standards specified in 722 and compliance with the Statutory provisions of the Low Voltage and EMC Regulations would provide a good level of protection for the designer. Of course if a manufacturer cannot do this you might want to look elsewhere. of course the products are required to be marked CA or CE or UKNI to be placed on the market for sale.
  • John Peckham:

    Yes Andy as the Note says, "it is the responsibility". So the designer or the specifier needs to demonstrate due diligence in the selection of the device. I think that obtaining a Declaration of Conformance listing compliance with all the standards specified in 722 and compliance with the Statutory provisions of the Low Voltage and EMC Regulations would provide a good level of protection for the designer. Of course if a manufacturer cannot do this you might want to look elsewhere. of course the products are required to be marked CA or CE or UKNI to be placed on the market for sale.


    JP raised this important issue. I went to NICEIC for some further advice. This is their reply;

    "Regulation 722.531.3.101 of BS 7671: 2018 amended 2020, requires that unless the protective measure of electrical separation is used, each charging point shall be protected by a 30mA Residual Current Device. Within the same Regulation it states that the RCD shall comply with one of the following British Standards; BS EN 61008-1, BS EN 61009-1, BS EN 60947-2 or BS EN 62423.


     


    There is some debate as to whether the RCD components installed within some manufacturers’ charging equipment comply with the above requirements.


     


    At this moment in time Note 5 of Regulation 722.411.4.1 places the emphasis of ensuring compliance squarely on the shoulders of the electrical designer/installer, as can be seen in the Note below;


     


    4b947293d0d986cb5a7347772db89ba1-original-image-20210323184041-1.png

     


    We would therefore agree with your suggestion of the installation of a recognised Residual Current Device upstream of the charging point, where any doubt exists. With regards to the issue of a lack of selectivity, so long as this does not cause a dangerous situation to occur, it would be acceptable. As the two RCDs are in series on a dedicated circuit, it would be difficult to envisage a dangerous situation, however as the installer this would be a decision that you would have to be satisfied with".