DNO connection

ce84021977c12a7ea512033714ca0b1f-huge-69d11d65-e54a-4553-b351-5a8d1daf4e4b.jpg
  • Typiod:

    broadgage not very easy to work on the cable live though is it.




    Yes it is, after proper training.

    The usual procedure is to cut about half of the armouring wires, and bend them away out of the work area, joint these temporarily with a suitable jumper cable. Repeat with the second half. NEVER cut or disconnect all the armouring wires at the same time. They may be carrying current.

    After jointing the four cores, a metal conductor is used to ensure earthed armour continuity.

    Encase the joint in a lead sleeve and make a plumbed joint between this and the lead covering of the cables. Fill the lead sleeve with molten bitumen.

    For added protection, a stout earthenware housing may be affixed outside the lead sleeve. Fill with more molten bitumen.


  • broadgage:

    Here is a radical idea. What about use of 4 core cables with a black neutral core, and red, yellow, and blue cores for the three phases. covered with PVC or similar insulating materials.

    Provide an outer sheathing of galvanised steel wires. This would serve three purposes. Firstly the robust wires would protect the insulated cores from damage. Secondly the steel wires would provide a metallic earth path back to the transformer. And finally, these metal wires would be in contact with the general mass of earth, thereby providing a very low resistance to earth.


    Radical - they shoulda done it years ago and far superior to this brown, black , grey with a blue N fiasco. We have become a thirld world nation


  • Former Community Member
    0 Former Community Member
    Encase the joint in a lead sleeve and make a plumbed joint between this and the lead covering of the cables. Fill the lead sleeve with molten bitumen.


    How many pages is the RAMS for this task?!!!


    Regards


    BOD
  • Given how many decades supply cables have to last, I would expect the steel wire armour to have disintegrated into rust long before the cables get replaced.


    It would be better to use 5 core 3P+N+E, and only use the wire for protection.
  • The pic is in Ireland. I assume, perhaps incorrectly, that the DNO (DSO) are bound by law to minimise danger in their network. In this case I am referring to the requirement to keep neutral effectively and reliably connected to earth. IS10101 2020 gives two examples of achieving this. One is to connect the PEN to earth to minimise risk in the event of a PEN break. The other demands that RB/RE is less than or equal to 180 (where Uo is 230v). RB being their combined electrode resistance and RE the consumer’s connection with earth via extraneous parts. Either way it seems to me that good solid connection of neutral to earth is required.