Chris Pearson:jimmyhorns:Hm! How is the compressor wired in?
32 Amp radial to Garage consumer unit to 20 Amp MCB to 6mm2 SWA to Single - 3 phase inverter to 3 phase motor of the compressor.
Using a 3 phase motor and running an inverter avoids the horrific start up currents and also allows speed control and avoids on-off cycling when the air drawn off is fairly constant. I designed/built the microcontroller circuitary that controls the inverter to predict / adjust demand.And with that level of sophistication you worry about a bit of wadding in a ceiling? ??
My 3 hp compressor eats 13 A fuses for breakfast (on start-up), but at least I have not adopted my chum's solution which is to insert a nicely turned bit of brass rod into the fuse holder. It may not be as bad as it sounds. At a steady state, the motor could not overload a 13 A fuse and under fault conditions, the MCB should trip.
Note, please do not do this at home. ?
Failed capacitor?
I cut the moulded plug off a commercial pressure washer and connected it using a 16 amp plug and socket protected by a C16 MCB, because it kept blowing fuses only to find it tripped the new MCB.
It was pulling around 57 amps on startup until the service guy replaced the capacitor.