Maximum Demand / ENA / EV Help!
Hello all,
This evenings issue relates to an EV charger install.
The supply cut out is labelled 60/80 amp so I called the DNO and asked if this could be uprated to 100 amp.
They have sent me the ENA EV application form which asks for the Maximum Demand including the new equipment.
The problem I have is the existing circuits are:
32A - 7.2 kW shower
40A - 8.2 kW shower
32A - Ring main
32A - 7.9 kw cooker
6A - lighting
6A - lighting
6A - security
Additional 32A for EV charger
So even with diversity I'm way over 100A, obviously in reality the diversity calculations are not appropriate as the client has never blown the cut out.
The smaller shower is not currently in use although they want to replace it for another one, I have told them this may not be possible.
The EV charger will have load management but I still need to put a figure on the ENA form....
Help appriciated :)
  • Sparkingchip:
    Red dye in domestic electric might make lighting a nice rosy colour.
    Just don't let them catch you using any of the red electrons to charge your car!
    Just be positive!
    BAD
  • D4G:
    Thanks for the input, although we did go off at a slight tangent ?
    Well, we have answered the question and now we are just nattering. ?
    So what is the proportion of discussion in here about EVs? 25%?
  • In November 2019 I was thinking towards the future regarding EV charging and after some discussion on this forum, I asked our DNO (Scottish Power) regarding our ASC or Agreed Supply Capacity.
    Their answer was simple, "Please be advised that we do not hold capacity information. We as the distributor would be responsible for upgrading the supply if this is required.
    An electrician would be able to advise what you have at the moment and if you require an upgrade."
    Following a further inquiry where I advised that the cut-out fuse was 80 amp seen visually when I asked the meter fitter, they came back with,
    "We only hold records for half hourly supplies. In order to assess what is in the property we would recommend applying for an additional load so that we can carry out a network study and advise you on the current capacity."
    I never pursued my enquiry, but if I did, do DNOs normally charge for that network study? If all it needs is a fuse to give a 100 amp supply, what is a typical cost?
    I'm thinking here of it likely being first come, first served until the capacity runs out...
    Clive
  • D4G:
    Hello all,
    32A - 7.2 kW shower
    40A - 8.2 kW shower
    32A - Ring main
    32A - 7.9 kw cooker
    6A - lighting
    6A - lighting
    6A - security
    Help appriciated :)
    The customer will not like it, but it’s the second electric shower that doesn’t even work that really messes the sums up, so they need to be told that it cannot be replaced like for like without a priority switch.
    If the installation needs load management to get the DNO to sign off the application then so be it.
    https://www.meteorelectrical.com/distribution-control/consumer-units-accessories-1/garo-priority-shower-board-choose-priority.html
  • AncientMariner:
    I am very slightly ashamed to say that that has been my approach. Get it while you can!
  • https://www.garo.co.uk/docs/2020/info/shower%20boards%20info%20sheet.pdf
  • Sparkingchip:
    I have told them that the replacement shower should be a mixer type or have a priority switch installed.  I'm sure if they ask someone else they will just fit it being as the second shower was fitted by someone in the first place!
    If the cut out is 60/80 amp as suggested, by the label then upgrading to 100A and by adding the EVSE with load management the system will be better off anyway ?
    I just need to suggest the MD is 81 amps or more.
  • Chris Pearson:
    D4G:
    Its all educational, maybe...?
    What colour is the existing cut-out, grey or black?
    BOD