John Peckham:
Chris
IET GN5 recommends a plastic insert in water supplies to outside taps that are use metal pipe work connected to a PME earth.
I have put a plastic joint in my incoming water supply just after the stop valve. I did this as. I have an overhead PME supply that gets thrashed by the local trees as it runs through the village during stormy weather. I have no gas or oil supply. I did this to prevent diverted neutral currents setting light to the house if the PEN became open circuit.
Hi John, please could you explain a scenario that could set light to your house had you not put a plastic joint in your incoming water supply? Thanks
John Peckham:
Weardbeard
When the PEN goes open circuit, and depending on the load on the network and the load balance on the network, current in the neutral will return to the transformer by any route it can. This includes bonded pipe work. These currents can be substantial and in some cases cause pipe work and conductors becoming red hot. Open PENs cause fires due to diverted neutrals and additionally over voltages damage and destroy connected equipment.
I have Ave an overhead PME supply to my house in Norfolk. That supply terminates in to the head at the front of the house. The copper water pipe enters my house at the rear of the house . Solid floor so the 10mm bond runs under the 200 year old floor boards. Without the insulated joint diverted neutral current under fault conditions could heat the bond up and set light to the wood.
Have a look at the virtual IET ELEX show at the PME presentation video and you will see a couple of photos of examples of fire damage due to PME faults.
That is why I do not ever install a main bonding clamp onto a lead gas pipe.
Z.
John Peckham:
Weardbeard
When the PEN goes open circuit, and depending on the load on the network and the load balance on the network, current in the neutral will return to the transformer by any route it can. This includes bonded pipe work. These currents can be substantial and in some cases cause pipe work and conductors becoming red hot. Open PENs cause fires due to diverted neutrals and additionally over voltages damage and destroy connected equipment.
I have Ave an overhead PME supply to my house in Norfolk. That supply terminates in to the head at the front of the house. The copper water pipe enters my house at the rear of the house . Solid floor so the 10mm bond runs under the 200 year old floor boards. Without the insulated joint diverted neutral current under fault conditions could heat the bond up and set light to the wood.
Have a look at the virtual IET ELEX show at the PME presentation video and you will see a couple of photos of examples of fire damage due to PME faults.
Thanks for the reply! Just to get this straight- you have a 10mm main bonding conductor connected to your water service but have installed a plastic pipe fitting in the service to prevent the 10mm from setting fire to your floorboards?