Hmm I had assumed that in normal operation the ring was closed and only opened at two isolators if one (or more than one adjacent) point at the substation required isolation..
Invariably they are operated as mid point open ring to limit fault current ebee.
Regards
BOD
Running open does indeed limit fault current but the main reason is to reduce the number of customers disconnected by a fault. A closed ring will just trip breakers a both ends on a cable fault unless it has a relatively sophisticated protection scheme which most do not. This protection normally requires circuit breakers rather than switches on the ring which is expensive. Running open means you only loose half the ring and most supplies can be restored by switching (increasingly using fault passage indicators to identify the faulty section these days).