whjohnson:
Chris,
If you are defining the house CU as 'the primary distribution board, how can you provide adequate discrimination via mcbs only?
Rather, I suspect you are saying exactly what I said!
There shouldn't really be any faults in the fixed wiring if it is done correctly and not abused.
Tripping off all of one of a series of outbuildings isn't the end of the world. A fault in any one distribution circuit would trip its MCB as intended, but the other ones would not be affected so there is some merit in having one distribution circuit per building as suggested by the OP although I see that the proposal has changed.
gbruell:
What exactly do you think is complicated? It’s essentially what you suggest in the first instance of feeding a board from another board but the original supply from a Henley and fused isolator? Plus seems sensible in my mind if I can to use RCDs in each board configured to prevent the previous outbuilding tripping?
The cascade of MCBs is all very well, but you probably will not get discrimination so if the last shed trips, all three MCBs will trip. At least the lights will stay on in shed 1.
RCDs don't help in the event of a short circuit.