Wet Location Body Resistance

Former Community Member
Former Community Member
What body resistance is assumed in wet locations vs dry locations? I have a feeling Table 41.1 does not take wet locations into account.
  • Former Community Member
    0 Former Community Member


    Do you know of the disconnection time in wet locations?
  • Table 41.1 is for dry location only.


    You will need to look at BS IEC 60479 series if you are looking at specific information other than dry location.


    In BS 7671 "wet location" is dealt with by special requirements in Part 7. Product standards take other approaches (including ignoring wet condition if the product is not anticipated to be used in that condition).