Combi Boiler.
Old Alpha HE CB 25.
 I have checked the pump, all o.k. Fan o.k. New hot water diaphragm- switch working o.k.
Circuit board o.k. Boiler tries to light but shuts off after a few seconds. No hot water. No central heating.
The strange thing is that when a hot tap is opened the central heating water pressure goes down. Is this a heat exchanger problem?
Thanks,
  • AJJewsbury:
    When the hot tap is opened at the sink, the closed heating (radiator) system de-pressurises to zero.
    And stays at zero when the tap is closed again?
    That's odd - even with the hot tap open the DHW pressure should be significantly higher than zero.
    Is there any sign of water escaping from the pressure relief valve? (usually through a copper pipe poking through the outside wall) - if the expansion vessel has failed a small increase in pressure can result in the PRV opening and so dropping the pressure. Of course the PRV should close again as soon as the pressure drops towards normal - but they're often a bit sticky and don't always reclose when they should.
    When we know more Andy, I will report back.