wallywombat:
The main difference between T&E and SWA is that damage may make the armour live along its whole length, compared to T&E where any "liveness" is just at the nail or exposed bit of conductor or whatever at the one point. Thus making any other minor damage to the sheathing or termination potentially far more dangerous
I would agree - if it were exposed. In this case, it is not. The cable is a relatively short run, clipped at a height where it is unlikely to encounter any mechanical damage.
I don't believe anyone on this forum doesn't disagree with the earthing of the steel wire, but back to my original post, I asked for regulation, not opinion, to support why steel wire 'Must be earthed' in this instance. To date, I don't believe anyone has come up with one.
You are making an assumption Andy, and that is that the sheath is undamaged.
So as far as I am concerned SWA has single insulated conductors within metal containment and that metal containment needs to be earthed
It’s easy to find guidance telling electricians to earth the armour of SWA cables, such as this: Providing automatic disconnection of supply (ADS)