Recommended wiring topology for multiple lamps on one switch?

As having an array of mains downlighters or spotlights in a ceiling is now fashionable, (rather than a single central luminaire), this begs the question of how to optimally and correctly wire them all up to the light switch.

In the case where one light switch operates multiple lights (as powered by from the domestic lighting circuit), there are several possible ways to wire from the switch to each of the lamps.

[It is taken as obvious that each lamp needs to be wired in parallel, with connections to the mains neutral and the switched-live wires.]


The (twin-and-earth) cable routing from the switch to all the lights and could be one of:

1) Daisy-chain   (the cable goes from the switch to one lamp, and then on to the next lamp, until all lamps are connected)

2) Ring    (like the daisy-chain wiring, but the final connection then links back to the switch to create a "ring main")

3) Star   (separate cables go from the switch to each lamp)

4) Tree   (i.e. a balanced spanning-tree, where the cable goes from the switch to two lamps, and each of them connect to two lamps, branching until all lamps are connected)

Each topology has different implications regarding the current distribution, and its associated heating losses in each segment of cable.

For example, a Daisy-chain topology has the highest current loading in the cable segment closest to the switch, but it uses the least cable; whereas the star topology has equal current loading in all its cable segments, but it uses the most cable.


Do the IET regulations recommend a particular wiring topology for particular scenarios, and what does everyone use in practice?

Thank you
  • And  Building Regulations limit where holes can be drilled in joists as well as the number of light fittings per switch.


    Andy

  • Sparkingchip:

    Why?




    I have only used these for installing LEDs where there is access from above e.g. from a loft to a bathroom or in a dormer bungalow with access above a kitchen.
    The wiring for the LEDs can be done away from the loft area, minimising time spent in those unhealthy environments.
    The connections are reliable and MF.
    The layout is neater than a daisy chain.
    The current distribution and Zs at each fitting is satisfyingly even.
    Overall fitting time is reduced but most of all it minimises the time spent in among dust and fibreglass insulation.

    It's a personal opinion.

    Mike.


  • Sparkingchip:

    Why?




    I have only used these for installing LEDs where there is access from above e.g. from a loft to a bathroom or in a dormer bungalow with access above a kitchen.
    The wiring for the LEDs can be done away from the loft area, minimising time spent in those unhealthy environments.
    The connections are reliable and MF.
    The layout is neater than a daisy chain.
    The current distribution and Zs at each fitting is satisfyingly even.
    Overall fitting time is reduced but most of all it minimises the time spent in among dust and fibreglass insulation.

    It's a personal opinion.

    Mike.


  • Sparkingchip:

    Why?




    I have only used these for installing LEDs where there is access from above e.g. from a loft to a bathroom or in a dormer bungalow with access above a kitchen.
    The wiring for the LEDs can be done away from the loft area, minimising time spent in those unhealthy environments.
    The connections are reliable and MF.
    The layout is neater than a daisy chain.
    The current distribution and Zs at each fitting is satisfyingly even.
    Overall fitting time is reduced but most of all it minimises the time spent in among dust and fibreglass insulation.

    It's a personal opinion.

    Mike.

  • Sparking chip. Andy,

    which building reg limits the number of lights per switch?

    Load I can live with but number I am not grasping a reason to limit.

  • Sparking chip. Andy,

    which building reg limits the number of lights per switch?

    Load I can live with but number I am not grasping a reason to limit.

  • Sparking chip. Andy,

    which building reg limits the number of lights per switch?

    Load I can live with but number I am not grasping a reason to limit.

  • A summary of Part L1
    • At least 75% of fittings must be low energy, defined as

                    - Efficiency greater than 45 lamp lumens/circuitW



                    - Delivering at least 400lm



    • Fittings less than 5W are exempt from the total count

    • Fittings in infrequently accessed areas (such as cupboards) are exempt

    • Halogen and GLS lamps are highlighted in the guidelines as non compliant

    • A single light switch should normally operate no more than six light fittings with a maximum load of 100 circuit Watts. 

    http://www.photonstarlighting.co.uk/regulations/partl/
  • A summary of Part L1
    • At least 75% of fittings must be low energy, defined as

                    - Efficiency greater than 45 lamp lumens/circuitW



                    - Delivering at least 400lm



    • Fittings less than 5W are exempt from the total count

    • Fittings in infrequently accessed areas (such as cupboards) are exempt

    • Halogen and GLS lamps are highlighted in the guidelines as non compliant

    • A single light switch should normally operate no more than six light fittings with a maximum load of 100 circuit Watts. 

    http://www.photonstarlighting.co.uk/regulations/partl/
  • A summary of Part L1
    • At least 75% of fittings must be low energy, defined as

                    - Efficiency greater than 45 lamp lumens/circuitW



                    - Delivering at least 400lm



    • Fittings less than 5W are exempt from the total count

    • Fittings in infrequently accessed areas (such as cupboards) are exempt

    • Halogen and GLS lamps are highlighted in the guidelines as non compliant

    • A single light switch should normally operate no more than six light fittings with a maximum load of 100 circuit Watts. 

    http://www.photonstarlighting.co.uk/regulations/partl/