Fault Finding-Comedy of Errors.
My customer reported that her washing machine repair man said that the protective device in the consumer unit was over sensitive as it kept tripping. I had installed it a few months back, it is a B16 R.C.B.O. It supplies just the single socket for the washing machine, nothing else.
Yes it did trip off after about 5 minutes when the machine was first turned on.
I could only detect a small earth leakage.
My customer said that she had plugged it into a kitchen socket via her extension lead to try that. It tripped off again very quickly, within 5 minutes.
A faulty washing machine I thought.
But no, it turned out to be a thermal overload trip on her extension lead that had tripped off.
I replaced the R.C.B.O. and tried the machine again in the kitchen socket that ran through a 30mA R.C.D. No tripping this time. Unfortunately the R.C.D. was faulty and would not trip off on test button or by my tester.
Then I tried the machine on the new R.C.B.O. It tripped it off in under 5 minutes. Two faulty R.C.B.O.s. NO I thought, that is just too much of a coincidence. A faulty batch?
After a while the machine ran without tripping off anything. I assume that damp got into the heating element and my forcing it to run dried it out. The problem is that when I took the top cover off the machine I could not access the heating element terminals, just E.L.V. circuit board stuff (5V-12V). The main ON/OFF switch is just an E.L.V. circuit board control not a mains switch.
Results. Faulty R.C.D. found and replaced.
Waste water hose leak repaired. But no water inside the machine.
R.C.B.O.s confirmed as being within spec.
Washing machine repair man will be advised of my suspicions about the electrically leaky heating element.
When fault finding check, check and check again to confirm the truth of the matter.
Although others' observations and comments may be useful, take them with a pinch of salt.
  • Peter Bernard Ladkin:
    This story is fascinating.
    I don't always have much luck finding causes of things going wrong with household kit (I am more with the bigger stuff, such as commercial aircraft accidents). But there is a manufacturer and a model number. Can't you just call the manufacturer's professional help line and say “this machine number XXXX trips the RCD at about the time the heater kicks in” and have the manufacturer run through the list of possible causes with you?
    Hello Peter, I am not the repairer. I was called in to assess if the R.C.B.O. was oversensitive. A washing machine repairer had called previously but could not find a fault. I did some tests to direct him and to be as helpful as I could. I do not repair domestic appliances any more as they are a pain in the back and too time consuming. The customer will call the repair man back. The ball is in his court now.
    As an aside, today I was working for a man aged over 90 years who had flown in Lancaster bombers during World War 2. He is as sharp as a pin and very interesting to talk to. As a young lad prior to joining the R.A.F. he was a telegram boy who used to deliver telegrams to relatives of solders serving abroad. He travelled on a bicycle. He told me of one lady, who upon opening the telegram and reading its contents fainted with shock at the bad news. After that incident he got a local neighbour to accompany him when he delivered telegrams to relatives of serving soldiers, to assist and offer comfort. Sometimes he cycled 50 miles per day.
  • I agree with kfh - keep clear! First, one has to disconnect all three services and drag the heavyweight box out from its den - always hard to do. Then take the lid(s) off hoping to identify what's amiss. Sometimes a new part needs to be ordered, so the tin box has to be struggled back in its den again. When the new part comes, drag it back out and try to make it fit, as the “policy of continual improvement” means the new part is often no longer identical.  Once done, the three services need to be temporarily connected for a test run to be sure it's fixed. It sometimes isn't……….que for some Anglo-Saxon language, hopefully out of earshot! Yes, I've been there more than once!
    To be fair, our washing machines are both over eight years old, both on RCBOs, and (touchwood), have never tripped. I think we're on borrowed time now.
    [PBL] This story is fascinating.
    [Z] Hello Peter, I am not the repairer. …
    Maybe not, but considering your pursuit of the issue I would imagine the client would be better off had you been.