Energy let-through for Type 2 MCB's ?
I'm nursing an elderly installation containing MK brand Type 2 breakers.
Does anyone have let-through energy curves for MK Type 2 32A MCB ? - Specifically LN5932.
Without any better data I'm likely to expect it to have I^2t no higher then a type C BS60898, and (based on 7x multiplier for instantaneous trip..), perhaps somewhere between a B and  C? Is that a safe assumption?
I have curves for Wylex BS60898 and for one or two other brands.
It's a bit of hand-waving I'd sooner not do if there are measured curves somewhere out there?
  • In the past with 2.5mm2 T&E cables with a 1.0mm2 C.P.C. protected by a 30 Amp bit of fuse wire for a ring, did we really have lots of melted cables or fires caused by that arrangement?
    Quote:
    "OK do the calculation for a 2kA or 1.5kA  fault current then if you prefer - it's still likely to be more than would reasonably be expected."
    If so the breakers and cables will be happy with a lower fault current. Or a large one, but not for long eh?
    The nice thing about fuses is that they continue to get faster as fault currents increase - so the energy let-through doesn't keep increasing - unlike MCBs where the speed of moving parts puts an upper limit on how fast they can open - so energy let-through tends to increase as fault currents increase. A 30A/32A cartridge fuse is probably perfectly adequate for a 1.0mm² c.p.c - unlike an MCB. BS 3036s will be a little slower so probably fail today's limits, but I suspect not by much.
    Pretty much yes - too low a fault current and the MCB won't open instantaneously, too high and the energy-let through increases beyond what the cable can withstand - it's only the limited area in between that's useful. Fuses are a lot simpler in that respect, not having an upper limit as it were (at least until you get to their breaking capacity).
  • Thanks Andy. There must be millions of '70s houses that still have 2.5/1.0mm2 ring final circuit cables installed. Perhaps a percentage of them still have hot wire fuses. I do not think that there is evidence that that arrangement was a real problem. After all it complied with the regs. and British Standards at the time of installation. Also, the M.K. range of M.C.B.s was of very high quality. Further investigation revealed to me that the range was upgraded to an M6 rating.
    The thing with the adiabatic equation is that it assumes that all heat is retained in the cable during a fault, and is not lost by conduction, radiation or convection, which may not be the case at all in reality.  So the equation is idealistic. This situation also makes it  err on the safe side.
    "I" in the equation refers to the R.M.S. fault current flowing into a fault of negligible impedance. Does such a thing exist in reality? I think that all earth faults will have some resistance/impedance that will limit fault currents.  Also, the disconnection time must not exceed 5 seconds.
    I have a gut feeling that the earth fault current with its arcing spitting and popping, will not be a steady fault current, but a varying fault current, rising and dipping with time. So it may not be accurately described as a "bolted fault current."
    www.youtube.com/watch
  • well it will still disconnect safely on a 1mm CPC at higher let through if the PSSC is quite a lot higher - the risk is not that it will not trip, just the insulation will be damaged and then the cable between the breaker and the fault will replacement.  That may be acceptable in many cases - the old cable would need changing soon anyway.
  • Why will the old 70s T&E ring final cables need replacing soon Mike?
  • You may need to change the reduced CPC cable with modern stuff because it has just been cooked with a bolted fault within a few metres of  the consumer unit. My point, perhaps not too well worded, was that there is really no need to change the cable on the off-chance of a fault, just because the adiabatic check is not met, until after the fault has occurred. The 1mm CPC racing a 32A breaker (and a 100A fuse as back up energy limit) will still operate the ADS and the 1mm2 copper will survive intact - it is the plastic near it that will not. The nightmare scenario that some folk imagine, of the CPC burning to open circuit and leaving a live fault, is not what happens. (though if the core area has been reduced by over tightening at a joint, maybe, but it has to be quite a noticeable core reduction)
    I probably could have worded that better the first time.
    PS, it is perhaps amusing to ask how far down a 1mm cpc do you need to be on a 230V circuit for faults of various magnitudes to become impossible, because at that current the voltage drop along that section of the copper alone would have to exceed 230V.
    Assuming 16 millioms per metre per mm2, i.e. cold cable. It is likely to be a touch higher for  cables that are already warmed by a load. This is the longest length of cable you may need to replace from this failure mode...
    6000A 230V = 38milliohms  = 2.38m of 1mm2 core. (and assuming all  the rest of the fault path is much fatter cable and infinite source current available)
    3000A 230V = 77milliohms  = 4.8m  of 1mm2 core. ( assuming as above)
    1500A 230V = 153milliohms = 9.5m  of 1mm2 core. (assuming as above)
    1000A 230V = 230milliohms =14.3m of 1mm2 core. ( assuming as above)
    For other cable sizes than 1 square mm, the length for the same resistance scales by the cross-section, so for example to get the same current limiting resistance with 2.5mmmsq cable you need 2.5 times the distance etc.
  • Have cables been empirically tested and results obtained to show the results of transient high currents due to faults, by say the B.S.I or B.A.S.E.C? Or is this just theoretical stuff?
  • no - its the adiabatic equation at work. What we calculate is how hot the copper gets for a given I2t, assuming no time for the heat to escape.
    for 1mm2 copper we should ask at the limit
    I2t <= K2S2 when k=143 what are we really doing ?
    well as I have said many times, 1mm2 copper wire is 16 to 19 milliohms per metre and amps2 times seconds are really joules per ohm- so we are looking at the number of joules of energy dumped into a given resistance.
    The second figure buried in there relates those joules to a temperature rise, and that is the heat capacity of copper, about 0.4 joules per gram.degree. or if you want to turn it over about 2.5 degrees rise per joule.gram. So how many grams in our 1m length of 1mm 2 Note that is 1000 cubes of 1mm 3 laid out end to end - same mass and volume as one cm3. Copper density is 8.8 times that of water or 8,8 grams per cubic cm.
    So,  we have 8.8 grams of copper, and regs say 1432 joules per ohm is only just OK, and we have 16 milliohms, well that is  1432 *0.016 = 327 joules - so in 8.8 grams a rise of about 90 degrees.
    From a 70 degree start this would certainly stuff the PVC if it was that hot for any time but is a very long way from melting the copper, that needs nearly a 1000 degree rise - so ten times the energy, perhaps 3 and a bit times the fault current. And of course the energy taken to break the bonds in the PVC does actually cool the copper a bit ;-) - the heating of the copper is never truly adiabatic.
  • J.P.J.  and the beer connection.....
    https://www.simscale.com/docs/simwiki/heat-transfer-thermal-analysis/what-is-joule-heating/