Cause of RCD not tripping with test switch
I have a strange fault where an RCD operates as expected when tested on the bench but when installed the test switch does not cause it to trip.
I have asked this on another forum but not really managed to get an explanation of what could cause it and why.
I have 3 RCD's giving the same fault, they trip satisfactorily when tested with an MFT when installed but test switch does not cause a trip with the downstream MCB's on or off.
My thoughts so far.
Unlikely to be the RCD as swapping has no impact.
MFT test creates fault current to earth, test switch creates fault current from live to neutral prior to sensor coil, how much current flows??
Insulation tests on installation gives about 1.04m ohm live conductors to earth at 250V on two circuits, 0.84 for installation at 240v this gives a leakage current of 285mA. Why doesn't this trigger the RCD, or do I have the decimal point in the wrong place?
The above is leakage current at 240V, but problem exists with CB's of, therefore presumably very limited voltage across circuit and current flowing.
Others have said its likely to be a neural earth fault. I can see the logic that the line is disconnected by the CB's and therefore it must be related to the neutral plus I could see that if there was a fault current in the neutral side it would balance the test switch current, preventing a trip. But what would drive the current as the potential difference between Neutral and earth is close to zero, and why would testing with a meter give a different result.
I thought about the RCD being bypassed in someway but I couldn't see any unexpected electrical connections.
I have considered DC leakage current, but would you get DC leakage with everything switched off? Maybe batteries feeding back through the charging circuit? There are led lights,  one TV and quite a few gadgets plugged in, but very limited compared to most, no car chargers or computers.
The house was rewired about 20 years ago with black / red PVC cable that looks reasonable. There is quite a bit of dodgy DIY, with fixed lights on flex, plugged in in to sockets, lots of extension leads and adaptors; unplugging these will be  a good starting point.
One strange thing I did find was that the house has a TT earth but when the main earth cable is disconnected at both ends I get an earth impedance of 0.3 ohms from the cable. Presumably a hidden connection to steel frame of the semi detached Cornish house, maybe with next door on TNC-S. Water pipes are bonded but isolated on entry to the house.
As some background this is on an old Wylex WSTM 100/2, 100mA type S rcd.
I realise I am going to have to disconnect circuits to break the problem down but would very much appreciate any thoughts on possible causes and theory behind the cause. I have a horrible feeling it's gong to come down to cumulative effect of multiple issues which are going to take considerable time and money to sort out. I won't be able gaurantee making 1 or 2 fixes will solve the problem and the customer has a genuine lack of money.
Any guidance on possible faults to look for and why they would cause the symptoms would be much appreciated, I am not a fan of just trying things without understanding the background science.
On a slightly different tack, I am considering failure of test button test as a C2 that needs resolving, am I over coding it and would a C3 be more appropriate? I am certainly not that comfortable with it as the owner has no way of knowing if the RCD is working and presumably there is one or more faults in the house.
  • If appliances work correctly in the house and there is no appreciable Voltage drop when they are on, that then confirms the supply side of things is O.K.
    Your R.C.D. does not need an earth to trip off via test button, as the test circuit  is connected L to N. Any internal house wiring problems will not affect the test button operation of the R.C.D. unless it is faulty, which I suspect it is.
    I believe that you are overthinking this problem.
    A new R.C.D. installed in the tails will solve the problem.
  • I am using second hand parts from one of the specialised suppliers, no new parts available.
    The reason I was going down the path of replacing the RCD is that I believe I am allowed to make a like for like replacement, even if it doesn't comply with current regulations. But if I use an external RCD is it still considered a like for like replacement?
    Is my interpretation of the regs correct?
  • I would install a new 100mA S type R.C.D. in the tails. Your customer will appreciate the fast remedial action. I have been in your position in the past when I was younger, and learned my lesson then. The more you delay and fuss about, the more the customer will become suspicious and nervous and lack confidence in you. You can't really rely upon the condition of old pre-used parts.
  • OK decided to go with your advice and ordered the parts, fingers crossed it solves the problem.
  • Very good luck Alan. Let us know how you get on please.
  • Hi All
    An update, as Zoomup has suggested I was over thinking things.
    Went  back to site this morning with various options in the van.
    Checked AC earth leakage current for the installation, only 2mA, I don't have a clamp meter for DC current. Supply polarity and voltage ok.
    Tested the RCD I had left installed with loads completely removed, test button still failed, then swapped it out again with the one that tested ok on the bench.
    It turned out that I had multiple faulty RCD's
    One was just ceased up
    One had an open circuit test button
    The one I tested on the bench was actually ok when I put it back in the installation, either the bench test cleared an issue or I got my RCD's mixed up when swapping them around.
    I now have a happy customer, thinking through the possibilities has taught me a few things and I will get to the right conclusion much quicker next time. Also I will be much more confident in my final conclusions because I have a much better understanding of the mechanisms at play.
  • Very glad to hear it all makes sense now. Coincidental faults can happen , but the relative rarity makes us doubt our sanity.
    And now as an aside you have some dead RCDs to look at the test resistor with a meter and or to crack open with your favourite hammer to look at the current 'transformer'  ring inside for a bit more  practical  'continuous professional development' as they call the more fun side of self-training these days.   Then they can go in the bin..
  • If I have a faulty item I usually scratch a big X on it immediately in a prominent position, or a big black marker X. Then I know not to install it. We have all been in your position at one time or another Alan.
  • This is an interesting lesson for all.
    Clearly the customer never (or rarely) tried the test button, and didn't notice that 2 were faulty, which were probably several years apart. RCDs are not that trustworthy, particularly if not tested or are oldish. Those who want to trust them need to understand that this may be misplaced, and that the test buttons must be used and work! Essentially it is never that the test button has stopped working.
  • Or that the test transistor as used in this S type model has failed. (Please see above).
    A thumbs up though to Wylex as the devices worked when an R.C.D. tester was used to trip 'em off. The build quality was very high.