HI
What bonding, if any, is required to metal benches / tables in a commercial kitchen...
No Graham, you have misunderstood, i
Or perhaps the English was not 100 % clear ... apologies, I would have anticipated something like "they, like metal window frames, are not extraneous-conductive-parts". In BS EN 60204-1 terms, these "tables" would be conductive parts of the machine.
Regardless, I have to fight the corner on this particular discussion, as we don't want people removing GNYE wires required by standards such as BS 60204-1 left, right and centre, from reading the thread.
In Noah's time we used to run the bonding cables at the back of tables or other equipment
I definitely remember that. And trying to convince people it was unnecessary, or, sometimes, dangerous, was really difficult, so I really don't have an axe to grind with my colleagues who are championing that particular issue.
I have not seen B.S. 60204-1. I do not expect that I can afford it.
Often said, but to be honest I don't accept this as a criticism in the UK. Most local libraries have a facility to access British Standards free of charge.
Some local councils provide read-only access to British Standards for library card holders, which can be accessed from your own home via the local library web-site.
This is definitely the case in Lancashire and Northern Ireland, but I'm sure there are other local authorities too.
So, please look a little more carefully.