EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • next issue - what date does 12 midnight belong to? is it 31st of Dec or 1st of Jan for example , you`d have to specify both dates to inform the reader which midnight it was. If you just gave 12 midnight and one date it would be misleading 

  • I still haven’t back from the vendor (they are an intermediary that provide landlord certification service/) that assigned the EICR inspector to me re NICIE technical’s views on the 2 C2s (recap - C2 not valid on bathroom lighting and the rcd C2 point needs to test supplemental bonding to confirm).

    But I have just received a quote from the vendor for remedial work and reissuance of a new EICR for less than 200 pounds. One thing that puzzles me is that the quote description only covers replacing two bathroom lights to IP rated. May seem silly to ask - does it mean that one can just replace the bathroom lighting to ip rated light to ensure compliance to RCD protection / supplemental bonding for lighting circuit condition? Thanks 

  • Fittings like these are still available and can be bought for £2.27 each including VAT.

    However add on a transformer, lamp and fire hood; and they cost more than a reasonable dedicated IP, fire and acoustic rated LED downlight that is more economical to use and is actually fit for purpose.

    These fittings were rarely fit for purpose and generally  badly installed,having said that I still have three in my bedroom in a bulkhead over the wardrobe doors, but they are mounted in such a way that the integrity of the ceiling above them is maintained. 

    These days I would not entertain fitting them in my own home or anyone else’s either for that matter.

  • One might equally well argue that it is 12 (am or pm) for a whole hour (to 2 significant figures).

    Absolutely, if you are using times that are truncated to the hour, rather than the example of a more common digital or analogue clock display often truncated at the minute resolution, the same logic persists.

  • However, it's also true that the clock time in minutes is "12:00" for 1 minute, and therefore (because dt tends to zero):

    One might equally well argue that it is 12 (am or pm) for a whole hour (to 2 significant figures).

  • The use of "noon" and "midnight" avoids any confusion.

    One can certainly use "12:00" for noon, but because of the ambiguity of "00:00" on Saturday, for example, nothing ever happens then in military circles. Events happen either at "23:59" or "00:01".

  • 12pm - there is no such time as 12pm or 12 am

    Not quite true ... I agree that neither of the monikers am (ante meridiem) nor pm (post meridiem) are valid at precisely the instant of noon or midnight.

    However, it's also true that the clock time in minutes is "12:00" for 1 minute, and therefore (because dt tends to zero):

    • at 12:00 ({midnight+dt}<t<{midnight+1minute-dt}) it's 12 am; and
    • at 12:00 ({noon+dt}<t<{noon+1minute-dt}) it's 12 pm.

    ... and that's Engineering Grinning

  • Lisa, How is a helpline not a consultancy? After all, do we consult a helpline or not consult a helpline? Aw well silly me.

    I am not as daft as this though "

    The technical helpline

    The telephone service typically operates on the following days and times:

    T: +44 (0)1438 765599
    F: +44 (0)1438 765526

    Monday and Friday, from 9 am to 12 pm and 2 pm to 4:30 pm."

    12pm - there is no such time as 12pm or 12 am - we had it drummed into us a junior school, senior school and apprenticeship/FE.

    Ranks alongside Grocer his Apostrophe methinks

  • That's a helpline and not a consultancy service Mike. Wink

  • fair enough. And  is not

    https://electrical.theiet.org/courses-resources-career/free-resources/technical-support/

    a form of consultancy service?. I've never used it but I presume somebody answers the phone if you call it before half four on  Friday.
    M