EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • Well I am slow when doing EICRs and I very very rarely do them, others are a lot faster than me but I have never met anyone who is that fast ever! 15 mins is what we call a "drive by", If we are lucky then we can visual sockets, switches, light fittings, in situ. Not open up a sample of same to inspect connections etc, not test (apart from plug in the meter for 1 type of test. That`s about it but that is not an EICR, it is a quick glance, that is all.

  • I don’t know what this guy is up to - perhaps he did test other stuffs but didn’t give me photos. I think my tenant is correct because she gave me a detailed rundown on what he did - he tested the fuse board and socket in living room and then for others like bathroom and bedroom he just switched on the light and cast his eyes and said there are issues need to change CU and left (all in not more than 15 mins)

  • Noted - thanks

  • I never had an EICR before - I commissioned him for a full EICR inspection 

  • I always like to think the best of people, but I am questioning what went on here.

    In the photo showing the socket ring continuity rest being carried out only the red live conductors are removed from their terminals, the black neutrals and the green/yellow circuit protective conductors (earth wires) are still terminated in their busbars.

    Then the test result on the tester is 0.14 ohms , but it doesn’t correspond with either of the test results recorded in the report.

    Far be it for me to cast  aspersions, but that looks like minimal testing to revalidate an existing Schedule of Test Results or even one from a flat in another part of the building.

    I will revalidate EICRs that I have done previously, knowing I have previously fully tested and inspected the installation; and I have carried out any remedial work required, but I do actually say that is what I have done on the paperwork.

  • Fifteen minutes is not long enough to test and inspect the installation, if the tenant is correct.

    Something definitely does not ring true, is it possible that the electrician had tested this installation previously some years ago and already had a test certificate or there’s a schedule of test results stuck to the front of the consumer unit or he had access to a previous EICR?

  • I said earlier in the discussion that RCBOs are expensive and not readily available for this consumer unit, based on having done an Internet search.

    You would also need to get the electrician to confirm that available RCBOs are compatible.

    To be honest I don’t think it’s worth spending money on the existing consumer unit trying to partially update it, as Chris Pearson says above replace it completely or as I said swap the existing components around in it to make use of what is already there.

  • I thought the MWC was just to confirm the work performed but this doesn’t seem to be the case from the quotations I receive - some even insisted on another EICR. It is really a headache! 

  • I’m in SE10. The EICR was sourced through landlord certificate services because they seems to have good feedback and I thought they would be assigning competent electricians.  I had no idea how long it was supposed to be. I only found out from tenant today that the guy only came in for 10-15mins in total (he clearly didn’t do much in that space of time, he slipped once during conversations to say he needs to come back to the flat to review the issues raised if he were to reconfirm that they actually are not issues! But of course he won’t admit to that now!

    Today I found out from talking to my management office that many people in the development has had EICR done and this is the first time they heard about the supplemental bonding issue and the electrical wirings are all in good condition according to their own engineer who has done extensive work and review on our development.

    I’m almost thinking whether I should go and change the fuse board in my flat (not knowing whom I may end up getting - this incident really give me a nightmare ) when everything has been working fine? But, I’m also sick of all this issue and wish to put this behind. So caught in a bit of dilemma now!

  • I’m sorry if anyone gets offended along these discussions.

    I'm certainly not offended, but unless you are in central London, those prices are a rip off. There should be no charge for an MWC. A new CU will include an Electrical Installation Certificate, which duplicates much of an EICR. It will keep everybody happy for the foreseeable future and when you sell, will be one less thing to worry about.

    I&T in 10 - 15 minutes is getting into the realms of fraud. Would it be too rude to ask how much it cost please?