Test certification & changes to supply characteristics
Looking for some guidance please, I am working on a construction site with a large temporary accommodation block due to be occupied asap. Due to design issues the HV/ LV supply has been delayed, to work around this a generator will be utilised as a short term solution.
This means testing & inspection will be completed via the genset and certs issued, when the new substation is completed the generator will be disconnected and sub-mains will be connected to the permanent LV supply.
This raises a question regarding re-test, in my experience usually best practice would be a full re-test, but some on the project are suggesting only the sub-mains will require re-testing.
To me this would probably come down to the designer signing the test cert and what they are prepared to accept, if only re-testing the sub-mains  I would think the final circuits Zs/ Pfc would have to be calculated as the previous test results/certs from the generator would be invalid due to the change of supply characteristics right?
So can anyone offer advice as to the options and is there anything in BS7671 regs that would be relevant to this situation, it’s also worth considering that if a EIC is issued for the generator can there be another issued for the LV supply? Is it possible to issue more than 1 EIC or  update the original or would be a condition report?
I’ve come across this situation before and it always seems to be a contentious subject with lots of different opinions, sorry for the long winded post, but would really appreciate some professional opinions on this, thanks Pray
  • Yes , but that kind  of is the issue,  there is one original design for the HV/LV substation. As mentioned the generator is an afterthought because of delays, the principal contractor has been difficult and have reluctant to produce a separate BOD for the generator but they will now the project has stalled. Its too late to alter the original COD, so you see initial verification against the generator will not align to the network supply in any way, the designer has stipulated a complete retest,  the only way I can see as an alternative would be to calculate Zs for final circuits but management on the project view this as doing the same task twice,  there's already an additional cost to retest the submains,  it's all a bit of a mess really
  • Presumably the accommodation units are being delivered to site with their electrical installations completed and dead tested.
    Presumably the dead testing won’t be repeated, so the initial EIC will be a bit of a hotch potch of a certificate anyway?
  • It rather depends what changes when the final supply is connected. As others have alluded it will really be PSSC and Zs and anyy circuits that are being paralleled up for the genset that may be split once power arrives.
    IF the first set of tests on the genset are done with a nod to this, (most gensets do not really have a PSSC that is as high as predicted by the test gear that does a small voltage drop test, preferring to stall or to drop out of regulation)  it should be possible to minimise duplicated testing.
    To that end a few more DC dead results of Z2 in some key places may be needed where the fault path will change on re-connection. Then a live PSSC/Zs test on the new supply, and the rest is probably calculation adding the DC test results and the new Zs,  and an inspection of the actual  new connections .
    The real question has to be could a dangerous condition sneak past such hybrid testing that would have been found on a full retest. I suspect that with care the answer can be arranged to be 'no'.
    What you write on the paperwork will also need some thought, as it will be dead tests of ABC on one day live tests with genset of XYZ  and then a little bit of final test on new supply.
    M
  • I will define a "Hotch potch certificate" as a certificate with several contributors and multiple signatories.
    The pre-fab accommodation units should arrive with their electrical installations completed and certificates for dead testing, then the temporary supply and distribution circuits should be assembled, tested and certified, before the whole installation is certified and handed over.
    This is more akin to a BS7909 installation than a BS7671 installation.
  • It's a good analogy but what about the change of supply characteristics from generator to network, only 5he sub mains to  the MDUs should need dead test again but about the final circuits within the block, full re test  or partial?