Where to install a surge protection device - single phase domestic / light commercial supply
A surge protection device can be installed in two locations:
1. The consumer unit. This is the easiest to install but it takes up two spaces which may not always be available.
2. The isolator switch. This is more difficult to install as it involves having to remove the big fuse but it avoids taking up two spaces in the consumer unit.
Does anybody have any more comments or advice on the best location?
Proteus sells an attractive looking isolator switch with a 2 module SPD although it is a bit pricey compared with SPD modules for consumer units. Has anybody got experience of it?
Who actually owns an already installed isolator switch? Is it National Grid, the utility company, or the property owner?
  • maybe both. but i was primarily thinking about the appliances themselves being more susceptible having more semiconductors in them nowadays
  • Mike, I think that you have taken whj slightly out of context. I assume that he means that mortgage holders have no option but to have insurance.
    In any event, quite a lot of people own nothing of any real value save perhaps for a phone and a telly.
  • There were plenty of appliances with semiconductors in them back in the 1980s. What I would say has considerably increased are permanently or semi-permanently connected electrical products with semiconductors in them like USB power sockets, LED lighting, home automation systems, alarms and CCTV etc.
    Has there been cost cutting in recent years so that modern appliances are less resistant to voltages surges than their older counterparts?
    What appliances that create voltage surges have increased in number?
  • If the insurers went down that route, then no one other than mortgage holders would ever bother with house insurance again.
    Not sure that I agree. Insurance companies can and do impose conditions such as the installation of fire alarms and burglar alarms. They can get quite picky with high net worth properties and I suspect that some may insist on periodic inspections or failing that, load up the premium.
  • I ask you - how many instances have there been whereby a house fire has been blamed on the electrics and the insurance company has refused to pay out on account of the cu being an old BS3036 rewirable with no RCD, no SPD and no AFDD present?
    Personally, I've never heard of such an instance, and I don't believe there will ever be one.
    RCD and SPD do not protect against electrical fires. AFDD are very recent technology so insurance companies still assume they are not fitted as standard.
    I have some semi-reliable information that insurance companies can refuse to pay out if the fire started in the consumer unit and it had a wood / bakelite / plastic case. If the fire started in the wiring then insurance companies will not differentiate between protection by a rewirable fuse / MCB / RCBO providing it had the correct rating for the wiring.
    Insurance companies can refuse to pay out for a fire caused by a faulty plugged in electrical appliance if the latest greatest consumer unit was installed by an unqualified person, or there was no Part P notification, even if it was technically compliant with wiring regulations, and the consumer unit was in no way responsible for the fire and could not have prevented it. They probably will pay out if a consumer unit with rewirable fuses was installed back in the 1960s by some unknown and long deceased person with unknown credentials.
    Are homeowners legally allowed to install their own SPD in a consumer unit without Part P notification?
  • I would be most interested to see your sources for the claims you make. I cannot believe that an insurance company would refuse to pay out under such circumstances. As for Part P, only lip service is paid to it these days. Fitting a SPD inside a cu would be the same as replacing a faulty mcb in my view, so no notification required.
  • RCD and SPD do not protect against electrical fires.
    RCDs are pretty good at spotting insulation breakdown that can lead to fires (both with and without arcing) especially where there's an earthed part in close proximity to the basic insulation - and that's reasonably common - not just in steel conduit and metal clad accessories, but even the humble T&E cable with an uninsulated c.p.c. is pretty likely to produce a detectable earth fault if damaged to the point where fire is likely. For a long time now the regs have recognised that ≤300mA RCDs provide some useful protection (e.g. 422.3.9, 705.422.7).
    .I suppose that SPDs may also provide some protection against the initial insulation breakdown that could lead to the parallel arc situation that AFDDs might be able to detect. So also providing some protection, if in a avoidance rather than detection form.
    How common is insulation breakdown in PVC? It happens with old rubber insulated cables but it's rare to find any still in use nowadays.
    There is the possibility of PVC insulation burning as a result of arcing, leading to a low L-E insulation resistance, where a sufficient current flows to trip a RCD before the MCB.
  • I suspect insulation break down in well installed PVC or polyethene is almost non-existent, unless there is some other factor.
    I'm thinking of things like cables exposed to bright sunshine lose their flexibility, and will perhaps crack if flexed - a problem for T and E on catenery perhaps,  but given the UK weather, only in on a timescale of the odd decade, and maybe never if on the shady side of the building.
    Damage by heating for wires stuffed in beside the pipes to the radiators is something I have certainly seen more than once, but neither of these are examples of 'well installed'.  The insulation test may or may not find either of these examples - a crack in a cable or a bit of browned off plastic, may be in a pre-cursor to trouble, but does not reliably result in a low resistance between L and E.
  • How common is insulation breakdown in PVC?
    Melted & charred PVC is common enough - just check the shower switch threads. As I recall the standard for testing AFDDs requires insulation to be charred before the the test - as clean copper to copper doesn't produce nice arcs at all - so I if it's unlikely an RCD will spot the problem it's probably similarly unlikely an AFDD will.