How are people tacking AFDD tripping?
In the past if I had a call out for a tripping RCD/RCBO or MCB there are well established procedures and tools to track down the fault.
These range from the visual inspection, insulation resistance testing, earth leakage measurement, RCD ramp testing and RCD time testing. It would not take too long to track down the fault whether it was faulty appliance, water ingress, damaged cable or even a duff protective device. The repair might have taken a bit longer but at least you knew where the fault was.
I had a call out this weekend for a AFDD that was tripping on a ring circuit. The new consumer unit (with 3- AFDDs, RCBOS and surge protection) has been in service the end of November and no issues reported. The customer did his own diagnosing and suspected the fridge/freezer as the circuit stopped tripping when he removed the appliance from the circuit. However, when he plugged the fridge/freezer in to another ring circuit with AFDD protection via a extension lead on a reel it did not trip. At this point I did not know what type of fault it was as the customer did not make a note of LED status on the AFDD.
The fridge has no damage and continuity and insulation resting testing all OK
Ring circuit was intact and insulation testing OK (greater than 500Mohm). The instrument readings were exactly the same as they were at the end of November. Plugged it back in and no tripping. I also ran a 1.8kW load on the same socket for a few minutes to see if I could get it to trip -  all OK.
Ten minutes after leaving the circuit tripped, I returned and from the flashing light sequence on the AFDD it was definitely an ARC fault. Reset the breaker and is was tripping regularly every few minutes.
I plugged in the fridge into another circuit, but this time with my much shorter extension lead. Then proceeded to inspect all sockets and checking tightness of terminals - no issues. Although there are some terminations not accessible for inspection.
Then I noticed the other circuit tripped (with fridge connected via extension lead) - so the conclusion that it is definitely the fridge. As the fridge/freezer is still under warrantee I advised the customer to contact the manufacturer. He plugged it into the original circuit in the hope to keep it running. It did not and I told him again to not run the fridge.
Later that night I get a message that now the other circuit is tripping every time they use the microwave -  not the circuit with the fridge and apparently fridge not plugged in.
At the moment I am not 100% sure it is the fridge and can't rule out a faulty AFDD or has the faulty fridge caused the  microprocessor in the AFDD to go faulty.
As a last resort I told them to switch off all circuits and main-switch and then switch-on one by one. Thinking that these devices have microprocessors maybe they need a restart every now and again - bit like my router at home.
Any suggestions on diagnosing ARC faults?
  • As I said before - swap the dastardly thing out for a RCBO on a temporary basis and see if that stops the tripping. If not, then it's something else.
    I wouldn't trust AFFD self-diagnostics as far as I could throw them.
  • Sadly I suspect that is all you can sensibly can do - you could try engaging the makers but I'd not be surprised to see sloping shoulders and 'it worked OK on the test bench- meets the spec so clearly not our fault mister'....
    I suspect something, on the same phase, but not in that flat, maybe not even in that building, only happens on Thursdays, and generates some supply side disturbances that trigger the AFDD off. Is it bin day or the perhaps gardeners come and have some big machine they plug in ?
    Electrically the thing can be defeated by suitable LC filtering to smooth the arc signatures, or whatever is being mistaken for that of course, but that seems a lot of nugatory effort and more than a bit silly.
  • I really want to do that given the fact we have tested all circuits and can find no faults whatsoever. I do feel boxed into a corner however as it is a 14 storey tower and dont want to be the person who takes these out and then a fire happens caused by an arc.
  • We have sent 2 sets back to the makers and they always come back saying they are performing as they should. I am going to give the tenant a call tomorrow morning to see if it trips tonight again. If so we will attend next Thursday. I did think it may be something like that, that for some reason a Thursday teatime is generating some sort of disturbance.
  • Could an upstream series arc trigger an AFDD?
  • It depends what is inside, and as it is all such a closely guarded secret we do not really know how well - I presume at some level, yes- there will be a similar current discontinuity if either the load changes or the supply... I'd like to think it looks at the supply voltage as well as currents, and so has a sense of direction, but the cancellation cannot be perfect. With another hat on it makes a possible attack vector to disrupt someone else's supply by tripping their breakers.
    Certainly in the US tripping from supply side events really does happen
  • I wonder whether the lack of test gear was considered by the regs committee?  I cant recall when testers were available for Surge protection Devices but if testers came later it does rather look like some learning has been lost.
  • I have installed SIEMENS AFDDs and have had no issues or false tripping.
  • Hey, as you've already taken significant steps in diagnosing the AFDD tripping issue related to the fridge. Given your detailed analysis, here are some further suggestions:
    Load Distribution: If possible, redistribute the load on the circuit to which the fridge is connected. This might alleviate any intermittent current spikes that could be triggering the AFDD.
    Dedicated Circuit: Consider providing a dedicated circuit for the fridge. This can help isolate it from other potential sources of interference or overloading.
    Cable Inspection: Check the cable connecting the fridge for any signs of damage, wear, or loose connections. A damaged cable can lead to intermittent arcs and tripping.
    Positioning: Ensure that the fridge is positioned away from direct sunlight, heat sources, or areas with poor ventilation. Overheating can potentially cause arcs and lead to tripping.
  • Thanks for the detailed reply. But the suggestions are not feasible in an existing installation with a newly fitted expensive kitchen.
    My only solution was to remove the AFDDs and replace with RCBOs. The manufacturer was not helpful.
    In the future if I am compelled to install AFDDs then will probably go for Hager as they seem to have the tools via an App to diagnose the fault and update the AFDD if necessary. https://hager.com/uk/p/afdd