Coding for Sockets Following EICR

Gents/Ladies, We have just had an EICR carried out on our premises (industrial) and the following Code C3 as been given for no RCD protection on sockets. I was under the impression that all single phase and three phase sockets up to 32amp were required to have RCD'S/RCBO'S or RCD sockets, unless a written Risk Assessment was issued. Is this correct?

  • The cost might be another matter, but I think that it would come into the realms of not reasonably practicable only if it threatened to bankrupt the company.

    Reasonably practicable does take into account cost (as well as time and trouble). The cost has certainly changed over the past 30 years ...