installing a separate neutral conductor

Hello

i have a customer who currently has a 250Amp section board with no neutral conductor. (a 3 core cable installed for 3 phase and a separate earth) some new equipment is being installed that requires a neutral. I've been asked to get a neutral into the box. 

is there any reason why i cant just add a separate neutral conductor. id argue its not best practice, but is it against regulation. ive had a good look and cant see anything that says no.

your thoughts and input are appreciated

  • What sort of cable and route is used for the 3 phases ? for BS 7671 a neutral needs all the insulation and consideration of a 'live conductor' but that does not mean that an insulated and sheathed or insulated and aluminium  armoured cable could not be used. (on the non BS7671 side the earth probably would be the neutral anyway)

    It needs to be run along side the lives - both to be obvious and to avoid current loop EMC type issues by having flow and return currents widely separated - more or less as you would do trefoil or quadrafoil with singles on tray or ladder rack.

    If the existing 3 lives are in an armoured cable,  there is a potential problem if  the armour wires are ferrous, as they form a magnetic enclosure, and the neutral current is uncancelled.  Even if it is the problem  may be avoidable -- how much neutral current is expected - how well balanced will be the load ?

    If it is one small 230V thing and a large 3 phase thing, it may be easier to bring in an auxiliary single phase supply, or look at a having a transformer either as 400V-230 step-down, or to regenerate a centre point of the 3 phases.

    but yes, quite often  the side-along cable can be done, with caveats.

    Mike.