Protecting cables carrying high earth leakage currents located in walls and partitions against impact
I am investigating options for getting solar PV installed at home, thinking about how I would like the system installing ready for when I get installers round to quote.
The house was built with a service void (plasterboard boxing-in) which runs vertically from above the consumer unit in the garage, up through the first floor into the attic and this void already carries a number of other cables, within a safe zone created by the void running up the corner of the 1st floor room and with an electric shower mounted onto the void. Using this void to run the AC cables from the CU to the inverter in the attic, protecting the cables from the weather/elements seems a neater long term option than running conduit or cable externally, given the 25+ year life of the solar installation.
The cable route from the attic to CU is a vertical drop, but its not a perfect straight drop down the back wall due to a joist and some pipework obstructions around garage ceiling level, requiring some change in depth as it passes through the floor. There's plenty of space to pull in a flexible conduit, following the route of the existing T&E cables. The void is quite deep, over 100mm, so fixing a flexible conduit to the wall in the attic should keep it comfortably more than 50mm from the surface from the attic through to the 1st-floor floor/garage ceiling. But where it passes around the joist and pipes, where distance from the surface is difficult to confirm, though at this stage it is passing through the floor/ceiling.
If it was a regular household circuit with additional protection from a 30mA RCD then singles in flexible insulated conduit, running in the safe zone created by the room corner and shower, appears to be acceptable, but with most solar inverters having high earth leakage currents which require 100mA or 300mA RCDs to prevent nuisance tripping, then this would not provide the additional protection from a 30mA RCD as required under 522.6.202 / 415.1.1.
Therefore the protection against impact would depend on the >50mm distance from surface, which while this is fine for most of the drop, is less clear where it passes through the floor. Using the options from 522.6.204; a rigid conduit (BSEN 61386-21), trunking, armoured cables or mechanical protection appears impossible because they are all very rigid and the nature of the route requires a cable system with greater flexibility.
So the permitted options if I want to get the cables run through the void, appear to be:
a) Satisfy the installer the distance from the surface will be >50mm so the additional protection from a 30mA RCD is not required and 522.6.204 does not apply, so allowing any inverter and all conduit/cable options.
b) Specify an inverter that can operate with a 30mA RCD for additional protection, the cable will be in a safe zone so fulfilling requirements of 522.6.202/415.1.1, though this appears to substantially limit the choice of inverter (I've only found one so far). Again all flexible conduit/cable choices become acceptable.
Are there any other solutions using a flexible conduit or flexible cable that I have missed?
One potential solution that is not stated as a permitted option in the Regs and I'm unsure why not, would be to use a flexible metallic conduit earthed at each end via a fixed gland, with a separate CPC, protected by a 100mA or 300mA RCD. And as per (a), clipped to keep it >50mm as far as possible.
This would be at no more risk of mechanical damage than the T&E cables next to it. In the event of a nail strike or impact, any penetration is earthed by the continuous metal conduit so ensuring tripping of the RCD without relying on a current to flow through the nail/screw/person causing the strike. The RCD reduces the required trip current to only 100mA/300mA so even though the flexible conduit does not satisfy the requirements of a protective conductor, it only needs to carry a very low current to trip the RCD. But that doesn't appear to be an permitted option, any suggestions why this combination would not be permitted?
  • Graham, thank you.
    A substantial part of the roof of my house is flat and the 2nd floor rooms can get quite hot in summer - say 30 deg C, maybe a little more. The difference in the loft space is that there is just bare roofing felt (and tiles) between the rafters. I have been contemplating insulating, but for energy conservation in winter.
    That notwithstanding, if the southern part of the roof were covered by PV arrays with a gap beneath them, wouldn't the roof be in shade?
    I am now thinking that before going further, it might be useful to install a temperature recorder (if there is any summer left).
  • I am now thinking that before going further, it might be useful to install a temperature recorder (if there is any summer left).
    That would be wise. Battery warranty is often temperature dependent, and both ambient and internal temperatures may be logged in the monitoring built into the battery itself.
  • Could be worth looking at PV Ultra cable by docaster cables.
    Personally I would not recommend the invertor or a battery system in the loft space for several reason
    Fire hazard
    Weight
    Heat in summer and cold in winter
    Regular maintenance
  • I understand your point of view, but I think the reason why it ends up in the loft is because it’s more convenient and cost-effective for the installers/clients. Also, the DC cables don’t have to run through the property, which might be safer.
    Definitely not the most sensible place, and as stated, because of temperature in the loft, there are certainly recorded inverter fires (without batteries).
    Storage batteries are also heavy, and there are a number of issues locating in the loft, including the problems it causes for fire service response in that location.
    I would strongly recommend against the loft for both, but certainly more strongly the battery. Best place for storage batteries in dwellings is outdoors, or in a detached outbuilding.
    A standard, PAS 63100, is currently in development for fire safety for the installation of batteries in dwellings to address the issues: https://standardsdevelopment.bsigroup.com/projects/2022-00181. I believe, at the moment, it's simply not clear enough for installers to know how dangerous some of the current installation practices can be given the wrong circumstances, and hopefully this standard will help address that.
  • I concur with your opinion. I think that the wiring regulations should be revised to prohibit this installation practice. However, I also think that installation work will continue to be done in a cheap and quick manner if there is no enforcement or oversight. I think that the industry needs to adopt higher standards and quality control measures to ensure safety and reliability.
  • If the code of practise and BS7671 state
    SHALL NOT install in loft due to (Thus resolving any ambiguity)
    Fire hazard
    Weight
    Regular maintenance
    Installers will follow what the designers of systems and manufacturers tell them to do.
  • I think that the wiring regulations should be revised to prohibit this installation practice.
    Not very likely I would have thought. The wiring regs (along with most other standards) started moving away from such narrow prescriptive stances several decades ago. Rather the approach is to state what need be achieved - and allow the designer/inventor to meet that in any way they like. So you might get something like: the equipment must be suitable for the ambient temperatures, have suitable access for maintenance, not pose an unacceptable fire risk, be suitably structurally supported, and so on (all of which is probably in the regs already anyway). Then when someone comes up with kit that is suitable for the heat, and wants to install it in a fully boarded loft with good ladder (or even stair) access, housed in a box that'll contain any likely fire or acid leak, you're not in a position of having to say no without being able to provide a sensible reason for it. No solution is perfect, often allowing a least-worse one is better than trying to prohibit everything.
    For me prohibition is a step too far.
    I wouldn't fancy working in some loft spaces that I have seen, never mind installing a PV system there. However, a walk-in boarded loft space is a different matter entirely.
    Where would you rather have your fire: down below in an integral garage, or up above in the attics?
  • If I had to choose a location for a battery fire I would say outside is best.  Again another discussion topic is the location of the battery outside.  Outside your front or back door is no good either as this will block your fire egress routes.