Caravan Site - Overheating supply neutral connection on pitch RCDs
Hi,
Am presently staying at a farm caravan park in south of England and the owner has shown me a problem he is having with some individual pitch electrical devices. Apparently, over time a number of the Type C  16A RCD devices have been affect by the INCOMING supply neutral connection overheating. Seems unlikely to be loose connection on so many devices and device are not tripping.
site is served by overhead 2 phase connection with single phase distribution to at least 3 sepeate areas built at different times. Pitches are served by buried SWA and marked up as “ring”. RCDs are British supplier and all other connections on the 30mA device are clean and unaffected. Are we looking at an harmonics problem or distribution system fault. All suggestions welcome (It won’t spoil my holiday) Thanks
Dave
  • if so then clamp metering over the 3 phases in turn and then over the neutral will reveal all.
    The electronics problem is perhaps easier to visualize in the time domain (thinking voltage against time like a scope trace) than the frequency domain (spectral analysis).
    Rectifiers feeding batteries and capacitors only conduct for the part of the time the AC waveform exceeds the battery voltage (or capacitor voltage), leading to a very discontinuous current concentrated near the crest of the sinewave.
    This leads to a trapezoidal waveform (flat topped 'acme thread') as the voltage drop on the line only occurs when the current is flowing.
    Now it is clear that 3 such pulses on the same wire cannot cancel in the way that 3 sinewaves offset 120 degrees in time would have done, as they are simply not overlapping, rather the neutral cable just sees current pulses like the live wires but 3 times more frequently with less time to cool in betwwen.
    In extremis, with no resistive loads to cancel, the current on the neutral current can be the sum of the 3 individual phase currents.
    Spectrally such current blips are composed of 3rd 9th harmonics etc but to describe it like that does not make the cause of problems quite so obvious.
    Low pass filtering effectively  smears the short pulses into longer ones, so there is some time overlap, but it is not a perfect solution, and gets bulky at high currents (after all the pulse energy has to be stored in the Ls and Cs of the filter and released slowly over the cycle period - more energy needs a bigger bucket)
    A better approach once you get beyond the main breakers is perhaps to treat the supplies as three single phases, each with a neutral the same size as the associated phase conductor  if you can.
    If harmonic currents are flowing in a single phase circuit then there is no more risk to the neutral than there is to the live conductor,.
  • The answer/ cause.............................................Harmonics
    But aren't the pitch hookups single phase?  I can see that in a 3-phase part of the system N currents fail to cancel out properly and so N can be higher than expected (max 1x the line current) - but in the single phase part of the system aren't the N currents going to equal the L current whatever it is (with harmonics or not). If the Ls aren't burning out, why should the Ns?
  • o I raised this problem quite some time ago with regard to a caravan camp site where the owner was having the local pitch MCB being replaced at random due to over heating of the neutral connection on the MCB.
    At the time I could not explain what was going on.
    Since then I have been involved in a more serious example of the same but devices were being burnt out, cables were melting and protective device were tripping randomly.
    The answer/ cause.............................................Harmonics.......................yep the one every body hears about but sometimes do not realise its a real world issue.
    At the moment, without further information,I can envisage two situations, either:
    (a) Perhaps I'm missing something, but if this is a single-phase RCD, that has been selected in accordance with BS 7671 (well, at least the latest version) ... If the issue is harmonics, that must present as a residual current at the RCBO ... or are we saying that the device ought to have been a Type F ?
    OR
    (b) The harmonics are on a "loop-in" (radial circuit arrangement) to the RCD, and it is on that ("line") side of the RDC that the burning occurs ?
    Could you be a little more specific ?
  • Hi Mike. The original post -  INCOMING supply neutral connection overheating. site is served by overhead 2 phase connection with single phase distribution to at least 3 sepeate areas built at different times. Pitches are served by buried SWA and marked up as “ring”. I’m not understanding how this is Harmonics ?  please  can you help with this one.
  • I'm not sure it is harmonics - hence my suggestions for confirmatory checks above.
    I'm also not sure what is meant by '2 phase' in this context - if it is really split phase (2 HV wires come in and the LV tx has a single primary, and a single480V secondary with the centre earthed) rather than a full fat 3 phase supply but with one phase unused (as I assumed initially), then the non cancelling argument does not apply, With bridge rectifier loads on split phase, the neutral currents do in fact cancel to a degree as the up and down phases actually do reach peak current of opposite polarity at the same time.
    I think we are missing some of the details that would allow more intelligent comment.
  • With bridge rectifier loads on split phase, the neutral currents do in fact cancel to a degree as the up and down phases actually do reach peak current of opposite polarity at the same time.
    Although some loads aren't as nicely behaved as traditional mathematical sine-wave assuming models might predict. Most caravans have what's basically a 12V SMPS come battery charger to run the 12V system and recharge the leisure battery. Rather than chopping up each cycle in the same way each time, it's perhaps more likely to run on a few-cycles-on then a few-cycles-off basis. Likewise triac controlled heating loads. Whether you still want to call that sort of thing "harmonics" is perhaps debatable, but it can have the same sort of effect on Ns. Given the on/off nature of the loads, the supply can often be "overloaded" in terms of instantaneous current without any overcurrent protection (or cable temperature) noticing, but the N might not get all the same "off" time to cool down.
    But still it shouldn't be noticeable in wholly single phase parts of the system.
  • But still it shouldn't be noticeable in wholly single phase parts of the system.
    Quite - however hideously non sinusoidal the current, the L and N in a 1 phase loop, will see practically the same,(actually  on a properly wired campsite, to within 30mA RMS)
    Only if the neutral incoming terminal has more than one cable in it, and there is a lot of current 'just passing by' not for that load, might there be a problem, and assuming L is similarly looped, then I'd not expect to see trouble just on N.
    And the immediate fix for that is not to over fill the RCBO terminals, but to use either Henley blocks or sets of Line taps in a box depending on what suits the arrangement, not harmonic filtering.
    Rather like 'Eddy Currents' and other well known Olympic skiers, an assumed problem with  'harmonics' may be invoked to cover cases that are too hard to explain - on its own, that does not make the explanation complete or correct - it needs verification.
    BTW for the pedants copy book, repeated bursted multi-cycle synchronous loads could be described as sub-harmonic distortion - switching every second cycle would introduce  a term at  25 Hz, every tenth cycle at 5Hz  etc.  Now, thinking about waveform distortion in the spectral domain is not that useful sometimes, and the time domain view is clearer - for sub-harmonics this comment  is even more true.
    There is a reason we talk about busses to Southampton arriving every 30 mins +/- some mins uncertainty rather than being a spectrum with a peak at 0.8 milli-Hz and some line width - both describe the same thing but the latter is not really a helpful description ...
  • Is this effect similar to the comparison between a lift motor and a fan motor (ECA) both rated at 20 kW with a running current of 35 A and a starting current of 175 A. While the starting current of the fan motor can be disregarded, the duty cycle of the lift motor must be taken into account due to its frequent start-stop operations within a short period. This results in a significant heating effect from the duty cycle, thereby increasing the equivalent continuous current.
  • A 20 kW motor would not have a neutral!
    There has still been no explanation why there might be any difference between L and N in a SP circuit.
    In terms of larger on-off currents being "thermally equivalent" to a smaller steady current, then yes, exactly so.  Say 200A being drawn 50:50 might be equivalent to only 100A (very roughly). The point then being that on/off on things on different phases won't necessarily be in sync, so the N might be getting 200A from one phase at one moment, then while that's off, be carrying 200A from another phase - so missing out on some of the cooling 'off' periods.