Maximum and Minimum fault currents

Bit confused, I was reading this in a book called modern wiring practices

Calculation minimum fault current 3P 3 wire.

Ipp = VL / 2zp

Ipp  - phase / Phase PSSC

VL - Line voltage

2zp inpedance of one phase only

So using 400V

In the design guide its.

Ief = Cmin Uo / Zx + CrZd + Cr'Z1 +Cr"Z2 + Cr'"Zpen

So using 230V


EIDG tells us A fault across three phases is considered the worst case....

and we get Cmax Uo / Zx +Zd

Again voltage to earth is used.

But basically a bit unsure why 230V is used to calculate 3 phase fault current and not 400V

Any help really appreciated. Thanks

  • Moderators, please could this be re-located to Wiring and the Regulations ? It relates to the Electrical Installation Design Guide, which is all about calculations to BS 7671.

  • Apologies for not noticing earlier. This should have been posted in the Wiring and the Regulations forum as it relates directly to BS 7671 and its guidance publications.

    I think you have mis-interpreted the phrase "A fault across three phases is considered worst-case" ... this is a three-phase bolted fault across all phases, not a  line-to-line fault.

    In a three-phase bolted fault across all phases, where all live conductors are connected together, and the fault current returns via Neutral or PEN. Hence, it is the line-Neutral voltage that is used.

    The maximum line-to-line fault current must take into account the impedance of each line and each phase winding, and therefore using the same symbols as present in Section 6.3.2 of the IET Electrical Installation Design Guide, 5th Edition, would be:

    Ipf(L-L) = UOC(L-L)/[2×(Zx+Zd)]

    As you point out, UOC(L-L)=√(3)×UOC, and therefore we get:

    Ipf(L-L) = √(3)×UOC/[2×(Zx+Zd)] ≅ √(3)×CmaxUO/[2×(Zx+Zd)]

    Hence:

    Ipf(L-L) ≅ [√(3)/2]×CmaxU0/(Zx+Zd) = [√(3)/2]×Ipf where Ipf is the bolted fault current across all three phases and neutral or PEN as above.

    Quite simply, because [√(3)/2] < 1, mathematically Ipf(L-L) < Ipf. Or in plain English, the line-line prospective fault current is less than the three-phase-to-neutral bolted fault current.

    Hopefully, this demonstrates why the maximum prospective fault current occurs not line-to-line, but between all lines and Neutral or PEN, and why U0 is used rather than U0×√(3).