Exporting final circuits
The Local Authority I work for as an Electrical Engineer is developing low carbon three story flatted residential properties with six flats in each block.
Each flat has its own single phase supply and there is 3-phase landlord's supply covering the common areas
The Mechanical Consultant has specified Air Source Heat Pumps as heating and hot water solution which is fine.
I am not at ease with the arrangement of the equipment the indoor unit is in the flat which is OK but the outdoor unt rather than being mounted on a balcony or wall of the flat it serves is located in separate out building.
This does not seem right as I have export a final circuit from the tenants consumer unit out with the boundary of their property through the common area then right outside the building to an out building.
Also the out building accommodate six final circuits all from different metered installations and also circuits from the landlords supply.
This seem highly irregular to me as all the guidance I have looked at for installed ASHP's states that in a flatted properties that ASHP's should either be a individual systems installed in the flats or a central system in which case it would be on common ground and be fed from the landlords supply.
Does anyone know of any regulations that advises against or prohibits final circuits from different DNO metered installation being mixed in the soom area / room? I have also asked this question to the DNO
Any feed back will be appreciated
Alan Gray
  • I the situation I am describing final circuits are leaving the customers property and going into common areas.
    I'd suggest that from the "common property"'s point of view it's a similar problem - having multiple sources.
    Circuits leaving the original "property" aren't unknown either (depending on what you define as the property) - obviously outside lights and garden circuits leave the main building, similarly supplies to outbuildings aren't uncommon, even if that other building is rented out or even is owned by someone else (where's there's some private arrangement to pay for the electricity used). At home I have my own supply to a street lighting column - which most casual observers might thing was well outside of my curtilage but due to the obscure local arrangement of unadopted roads is actually on my land, so for anyone without access to my deeds, would certainly appear to be 'exported'. (It it labelled inside so it's clear where the supply comes from if anyone takes the outer cover off).
  • I have my own supply to a street lighting column
    How quaint! Isn't it more traditional to go the other way? :-)
  • Thanks for your reply, The Property is a block of flats there is one three phase landlord supply which serves a lift, close lighting and external lighting on the surrounding land to the boundary of the plot, There are six individual metered DNO domestic single phase supplies one in each tenants property.
    It is my view that single phase 230V LV final circuits from the tenants consumer unit only serve equipment within that individual flats and that 400 / 230 LV final circuits from the landlords supply only serve equipment located in the common areas. In the situation I am dealing with there is a proposal to bundle final circuits from all installations in a single location
  • Hi Alan
    Could you use
    to power the ASHP.  Then meter it back to the tenants?  I would also consider the Landlords supply be specified with a design consideration for EVSE.  This could help resolve the issue of differents supply in one external location with possible different CPC/Earth.
    Next part of the puzzle will need to be some kind of RF to control the ASHP from within the flat.
  • In the situation I am dealing with there is a proposal to bundle final circuits from all installations in a single location
    That is more worrying. I had assumed that the cables to each unit would run separately, but if by "bundle" you mean place in the same containment system, there is indeed a problem.
  • I think at the least it needs a policy of one flat, one electrical box, one isolator, all clearly labelled up and separated, even if in the same outbuilding.
    At best it will end up looking like one of those basements you get in small blocks of flats where all the meters and sub-mains converge.