18th Edition Consumer Units / Distribution Boards
I am extending an existing electrcial circuit in my house to a shed and garden. A registered electrician will be completing the work but I am tasked with buying the materials. The circuit will be fed from the existing house distribution board to an additional distribution board to feed the shed and garden sockets. The additional distribution board will be outside as a temporary measure until I build a brick garage at which point a permanent installation will be made and the distribution board moved inside. I believe the minimum I need for a board located outside is IP44, I am unable to find a metal unit with an IP44 or higher rating, they are all plastic. The oustide distribution board will have an isolator switch and an MCB to protect the shed/garden circuits. My question is do the current regs require all distribution boards to be metal or do they allow plastic when it is a downstream of the main house board or outside? Any other thoughts / input gratefully received?
  • "The CU/DB (consumer Unit / Distribution Board) should use Main Switch & RCBO and not MCB. "
    It certainly could - I think to say should which implies must is a bit strong, certainly there should be RCD/RCBO protection somewhere, but that could be at the house supply end.
    It rather depends what is going in the garage eventually, if for example it really needs separated power and lights circuits, or if it needs data cable as you suggest for that matter - it is nearly twice the price of the normal SWA of the same capacity.
    What you describe may be a bit more gold plate than is needed.
    Also if there is any chance in the future that there may be an EV charger or a service that needs bonding (like a water pipe) then the decision to export the house earth or to make a TT island needs to be made, as indeed the total load and the distance will determine the cable size in the normal way.
  • Yes, that is correct. They have 3 ways, two of which are populated.
  • I use plastic WISKA enclosures for outbuildings which are damp and not 100% weatherproof.and then populate them with whichever spare devices I have to hand, usually a RCD main switch and a couple of MCBs left over from a old consumer unit suffices well.
    These things are bulletproof and waterproof.
    www.sparkmonkey.co.uk/.../wiska-1306br-w-6-way-ip65-distribution-enclosure-with-din-rail
  • worth considering using something like Docaster EV ultra it can deliver power a data via cat 6 in one neat bundle to the shed.  Use it for WiFi.
    I'm not sure that'll meet BS 7671 requirements for 100mm separation of buried power and comms cables (528.2). (To be honest I'm not that keen of twisted pair inside the same sheath/armour of mains cables even above ground.)
  • Docaster EV ultra
    Below is from the EV_Ultra_Datasheet
    Proximity of electrical services (extract from 528.1) - Except where one of the following methods is adopted, neither a Band I nor a Band II circuit shall be contained in the same wiring system as a circuit of nominal voltage exceeding that of low voltage, and a Band I circuit shall not be contained in the same wiring system as a Band II circuit. (i) - Every cable or conductor is insulated for the highest voltage present.
    EV-Ultra® consists of power conductors and data cables that are rated to the same nominal voltage – therefore segregation of power and data is not required.
    Proximity of communications cables (extract from 528.2) - Special considerations of electrical interference, both electromagnetic and electrostatic, may apply to telecommunication circuits, data transfer circuits and the like.
    EV-Ultra® has been designed with these considerations in mind, it incorporates screened, twisted pair data cables and is also constructed with a lay length that reduces interference. Laboratory and on-site installation tests have also been conducted and no interference or degredation of signal was recorded.
  • So they say, but I still don't see how that meets the requirement for 100mm separation, or "a fire-retardant partition... between cables, e.g. bricks cable protecting caps (clay,concrete), shaped blocks (concrete), protective cable conduit or troughs made of fire-retardant materials)" for cables underground.
  • you could ask them that question
    sales@doncastercables.com
  • Well it does not need to, as the makers instructions take over from what is after all a generic standard aimed at keeping bell wire out of the consumer unit and similar stupidity - the same 'problem' could be seen with the wiring for every phone, pabx and fax machine but it is solved.
    In this case Doncaster are the ones to whom you pass the blame ;-)   You should be careful at the ends however, what you do not really want is to be stripping and terminating the network and mains ends in terminals in the same box.
    If need be a dummy box with nothing in it but glands, where the data and power cables are split their separate ways, is a neat way to handle that one.
    The EMC  concern is interesting and hard to prove, but I can believe it causes very few problems in practice.
  • the same 'problem' could be seen with the wiring for every phone, pabx and fax machine but it is solved.
    But they're not (usually) underground - which is what 528.2 is aimed at.
    Even above ground I usually see something a bit more substantial between data and mains side than a single layer of basic insulation and the data cable sheath (a sheath on the LV cable for instance, or a bit of clear space)
  • True and it feels better with a bigger gap.- but if that basic insulation on the mains wire, and the cable sheath on the data cable had been tested to the same flash test voltages as the other 3 phase cores, then a lot of that worry should abate.
    I agree it may 'feel' wrong, but I'm pretty sure it is no more dangerous than many other things we are unused to and do not like, that on close inspection are OK really, like perhaps the two phases behind one light switch without a 400v label, or the sockets in bathrooms moving ever closer, that UK folk get upset by.
    It is (as often with these sort of things) in the hands of the manufacturers.