Alternative solar supply available at point of use Domestic kitchen

Hello newbie : 

Imagine Domestic kitchen Usual array of sockets and under counter appliances

Wish Introduce  Alt solar supply sockets alongside existing grid supply sockets , Thus : User can select alternative ( solar ) supply as opportune arises  at point of use ( battery storage/ inverter system)

Eg plug microwave to alternative socket  as power opportunity ( battery charge is available ) 

(Alt supply sockets are entirely dedicated from inverter as typical OFF grid system ) 

Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs? 

Remark : similar to external generator supply but with NO changeover switches . Outlets are dedicated 

thanks Ms Otis 

  • I think I'm with you - you just happen to have two distinct LV systems inside the same building. I'm not seeing any fundamental problems with that (I think Graham is considering the possibility, all too common with some of the latest inverters, that they can do all kinds of clever things like taking over from the grid supply during a power cut, or that the battery could be charged from the grid supply). So we're not talking either about a switched alternative nor a parallel source.

    You will need suitable equipment of course - especially your chosen inverter will need to be capable of running as a TN-S system with a N-PE link (as you'll be feeding >1 appliance) (many smaller/cheaper inverters, indeed petrol generators, are configured as unearthed "separated" system and aren't suitable for feeding multiple appliances via a fixed installation and may or may not be convertible) Your "off grid" system will need a reliable means of earthing - i.e. a local electrode. That does NOT make it a TT system though (for that you'd need two electrodes, one for the "source" and another separate one for the loads) and as it shares an environment with the grid supplied system, the two earthing systems will need to be connected together. You electrode will look like an exposed-conductive-part to the grid Earth (like a bonded water or gas pipe) and likewise the grid Earth will appear to be no more than an another exposed-conductive-part to your off-grid system. (That does bring in some requirements - e.g. the conductors from the grid's earth to your electrode are treated as main bonds for the grid system - so the minimum conductor size is a fairly chunky 10mm² even for a typical domestic - potentially larger. Physically that's almost certainly unnecessary as the resistance around your electrode will limit the current to something quite small, but the regs don't recognise that).

    I'll try to draw a diagram when I get a chance - a picture can be  lot clearer that words...

           - Andy.

  • Question remains IS this possible and so avoid changeover switches converting alt source to island   Grateful thanks  again to all still on this thread

    Only if the inverter is arranged to prevent back-feed of any description to the grid - which is possible in non-separated inverters, or inverters that contain transformers.

    Note that semiconductor devices are not (currently) considered to be isolators.


    There are still provisions regarding earthing of both systems to conform to IEC 60364 and BS 7671 in the UK.

  • thanks again Andy and all I was getting excited there it was do able > BUT  These examples seem to be all about  changeover switches Isolating

    circuits from grid / reconnecting to inverter : 

    If your still with me Please check again the concept : Perhaps I am breaking new territory If you would please indulge me one more time : to be sure 

    GO and stand in your kitchen : Look at the socket outlets  Now imagine next  to EACH is installed another : These added sockets to be fed directly and independently  connected via solar/ battery  inverter (separate distribution board)  All separate: wiring : everything: 

    These "alternate"  sockets go live whenever  ( you)  consumer turns on the inverter . The grid sockets are also live same time. Now imagine you consumer go and choose alt supply source by simply unplugging any appliance eg microwave and plugging into adjacent "alt" socket: Thats the point of it 

    No changeover switches to existing loads  Inverter system was thought as fully  independent : 

     OH  damn !!!!  by your good observations  we see a problem with earthing to appliances  IF  we introduce a separate  TT earth. One chassis at different potential to others.  

    Last ditch  is could we avoid  sperate TT earth and simply link the  inverter earth system to incoming grid earth. ?  ( I think you are saying that would mean BOTH Ground and Neutral  were linked.  Inverter to grid incoming.  

    Question remains IS this possible and so avoid changeover switches converting alt source to island   Grateful thanks  again to all still on this thread

    Ms O 

  • There should be no great technical issue there.

    Except the way some inverters on the market are arranged. It really depends on the arrangement of the inverter itself  whether this is possible (because in connected modes of operation, there is one side connected to the DNO supply).

    There might be a way of putting a manual changeover isolating switch in the installation, that can switch over the earthing arrangement at the same time as disconnecting the grid.

    The Linking the off-grid system's earthing system to the grid's is precisely the way to go

    In fact in most installations it would be a requirement because of Regulation 411.3.1.1.

  • So with TT earth on inverter there could be a potential difference between m-wave chassis and fridge  Both easily in reach.  So unless I can link Inverter earth to grid earth . Guess thats the no go.

    There should be no great technical issue there. There are plenty of buildings with more than one DNO supply - these things can be done.

    On a point of order, the inverter will normally have a solid metallic connection to it's electrode (via a N-PE link) - which will be the only reliable earthing point on that system - that makes it TN-S rather than TT. (Remember your invert will be the source - i.e. takes the role of the substation/transformer in conventional earthing arrangement diagrams.)

    The Linking the off-grid system's earthing system to the grid's is precisely the way to go (there are a few technicalities to get right - e.g. on conductor sizing - as an earth electrode on one system will appear to be an extraneous-conductive-part to the other) - but all eminently doable.

        - Andy.

  • Map : thankyou for encouragement : Perhaps its been difficult to get the concept understood : But now in between the comments  can see a problem 

    The concept is BOTH alt and grid sockets could be live and in use simultaneously  :  User has choice at point of use. So eg the micro wave could be plugged into the alt supply socket  whilst the fridge on grid . So with TT earth on inverter there could be a potential difference between m-wave chassis and fridge  Both easily in reach.  So unless I can link Inverter earth to grid earth . Guess thats the no go.

    Going to point myself to the solar guys on this channel. My supplier is a dedicated OFF GRID person. Not standby or anything else   Not happy I've had to drag all of these issues out of them. Maybe someone can point me to a more friendly supplier. Though it does look like changeover switch or nothing. Nasty clunky ugly things  Plug in point of use so much nicer. and cheaper. ... cin cin and thanks again for all your help   Ms O .  

  • your local earth electrode will not be on the fence, just underground ;-) all you will have on the surface once it is all over is a small access cover at the top of the rod or rod. Neater than this one, it is about 15cm by 15cm the rod is 4ft (1.2m)long, and the diameter of your thumb,  and drives in just like a big nail. Just avoid the drains. and the gas pipe ...

    Oddly I have been looking at a battery and solar system something like this - a colleague at work keeps telling me how good it is...  And most of the companies I have spoken to have no problem putting the battery indoors, in the loft or indeed in an waterproof cupboard on the roof of my attached garage (!), so your suppliers sound like they may be more nervous than many. Cable underground in ducting is a perfectly sensible thing, and done all the time so again I am surprised.

    That said all but one of the folk I have been talking to did  wither a bit when I start asking deeper questions about fault currents and Island modes, and I rather fear/ suspect many work by repeating the same recipe rather than a deep grasp of the design fundamentals.

    (my own domestic electrics are a slightly non-standard shall we say... )

    Mike.

  • So I give up : 

    That's a shame Disappointed

    .Proposed underground cabling . Supplier ( Victron kit)  refuses any guarantees if I do that 

    That sounds peculiar - electrically underground cable isn't that different to say clipped to a fence.  I wonder if something has been lost in translation - or is the underground cable for the DC solar side?

    3. Supplier now states I will need to supply separate earth electrode 

    That bit makes sense at least.

    Mind boggles at some "Brunel tunnelling  for earth electrode  

    In most situations, hitting in a 4' long 3/8" diameter rod into the ground with a hammer suffices. Traditionally a few inches were left above ground to make the connection, but the preference these days is to sink it into a small pit with a lid over - still you're only talking about digging up less than 1 sq ft to a depth of a few inches - hardly IKB's territory and not a lot compared with digging the trench for an underground cable. (For my detached garage, which I wished to TT, I used one of the access chambers for the underground supply cable to house the electrode - two birds with one stone as it were)

     Seems in USA back up generators are not novel.

    Not entirely unknown this side of the pond either - the subject comes up i the Forum fairly regularly. .Usually as a switched alternative though (so supplying all (or most) of the normal house wiring, rather than independent dedicated circuits) but it's all horses for courses. The entirely off-grid community has a presence here as well.

    rather than petrol perhaps

    Most true backup generators tend to be diesel rather than petrol - as petrol "goes off" after a relatively short time (in a matter of weeks or a few months, the lighter more volatile components of petrol evaporate, and the remainder doesn't work as well) - just as an aside.

       - Andy.

  • PS Still think the idea has great  meriit for smaller domestic affordable solar back up 

    The UK does permit "backup" ... but the right product needs to be selected. There are products on the market that can be installed in a conformant manner.

  • Dear all  Wish there was wat to thank everyone for contributing and I guess close this thread .  So hope this suffices:

    Not familiar with solar electrics Was relying on a supplier but with me locally laying the groundwork  Now we have more constraints 

    1.I stipulated would not tolerate a volatile lithium battery in my house  ( therefore would site inverter etc in garage at rear of my garden)

    2.Proposed underground cabling . Supplier ( Victron kit)  refuses any guarantees if I do that 

    3. Supplier now states I will need to supply separate earth electrode 

    Not prepared to disfigure may garden with exposed wires nailed to fences , Mind boggles at some "Brunel tunnelling  for earth electrode  

    Is it also most of you express disquiet  in one form or another Not all understood. 

    So I give up : 

    PS Still think the idea has great  meriit for smaller domestic affordable solar back up    Believe power starvation ix coming . I cannot see the merit of anything grid tie . Seems in USA back up generators are not novel. Though solar rather than petrol perhaps is.

    With thanks to you all 