Long meter tail upgrade, no nice solution comes to mind.
Hi All.
Thought I'd open this one up for discussion as I'm sure some of you can come up with a nice solution.
I've been given a friendly notice that i need to do something about the meter tails in my house by my DNO following the installation of a smart meter. They're the wrong gauge for the master fuse (16mm2 on a 100A fuse) and too long, about 4m. I'm having a job coming up with a solution I like. The current installation is original from when my house was built in 1996 and has gone unnoticed until now.
The meter is in a box on the front wall of the house and the tails exit this, run up the inside of the wall and over the ceiling of what was originally a bin cupboard in an uninsulated roof space before entering the distribution board directly though the hallway wall. The logical thing to do would be to protect the tails by replacing them with SWA but I have two problems with that. 1 that I have no way of terminating the SWA in the meter box without invading the DNO's space and 2 I'm not confident in brining in SWA from behind the board, as I'd effectively have to terminate it long and push some excess back into the roof space, and end up with the SWA termination in the wall screwed to the back of the board. So I can see this option needing me to bring the SWA in from above or below the board which would be ugly as sin in my hallway, doubly so as it'll have a bend radius easily measured in miles.
So I've considered using Steel Conduit instead, as that should be as tough as SWA. However unless I've missed something the largest I can get is 32mm OD which has an ID of circa 27mm. As I'm expecting some quite high temperatures in the roof space during the summer 25mm2 (rated to 101A if I'm reading Appendix 4 properly) could well end up under rated in the summer, so I'd be best to use 35mm2. This has a max OD of 13.5mm according to Doncaster cables meaning it'll be tight getting 2 down it.
I considered using XLPE Insulated 25mm as that can run hotter but of cause there's the 70 degC conductor limit of the board so it's not a help.
Bringing my back to SWA again.
I don't want to put joints in above the bin cupboard as there's no way of inspecting them.
So any other ideas of what I could do to protect the cables sufficiently to ignore the limits?
Thanks in advance.
  • yes it was under the floor boards
  • sounds tricky. How did you deal with the joists? Did you notch or drill them?
  • I was lucky that there was a gap between joists formed between the original house and the extension, which got me half way. Still have a dilemma for the second half of the run, my choices are:-
    Continue same line, which involves running in parallel with heating pipes for about 2 m, need to do some cable calcs
    Failed so far, but see if I can get the cable in a cavity wall void below the pipes
    Divert the cable in to some joist notches currently occupied by a redundant gas pipe, reduces run next to heating pipes down to 30cm
    Drill new holes in joists, proximity to existing notches, holes and end of joist would breach building regs
    Whatever I do won't be ideal, but better than the what was there.
  • Continue same line, which involves running in parallel with heating pipes for about 2 m
    Are the pipes lagged/insulated.  If not insulate the pipe and run cable along side.  That way you are helping the customer with heating efficiency.  These things are always tricky unless you are there or have pictures.
  • Divert the cable in to some joist notches currently occupied by a redundant gas pipe, reduces run next to heating pipes down to 30cm
    Always use existing notches or holes if you can. Even if they do not comply with the Building Regs, you did not make them, so they are not your responsibility.
    As Sergio says, insulate the pipe, or improve it if already insulated.