Is my theory about earthing correct?
Had a discussion with my colleagues at work today around the theory of removing all earthing.
This is my question:
If I poke my finger into the live terminal of a 230v socket, the line current travels through me, through the floor (earth), back through the earth to the supply transformer (because the transformer star point is also tied down to the general mass of earth) the fault currents travel back into the transformer star point and hopefully the completed path is of low enough impedance to be able to blow or trip the protective device serving the socket I touched.
Now. If the transformer star point WAS NOT connected down to earth, there would NOT be a return path from the socket I've stuck my finger in, back into the star point of the transformer and I wouldn't be able to recieve a shock as there is no complete return path.
Is that correct or not?
So following on from that, my question is: why cant we just isolate all transformers from earth and remove the risk of a "line to earth" shock? After all, this is exactly why we use SELV transformers in bathrooms no????
Obviously you could still get a line to neutral shock, but that's got nothing to do with the question I'm asking here.
  • The exact current path is a mixture of the parallel paths of conduction (resistive) and displacement current (a catch all term for the capacitances , where the body is one plate, and the conductive bits of the surroundings form the various  other 'plates' and the dielectric filler in that capacitor is the air, and/or the insulating bits of the local environment)
    You are quite right, on a dry wood floor, the main effect will be displacement  - and unless you are very slim I'd expect you to be a few hundred pF to the 'plate at the end of the universe' and at 50Hz the current will be just about enough to light a neon screwdriver or operate a volt stick, but not really enough to be more than a very weak sensation, maybe not perceptible.
    So with well insulated footwear and taking care to be nowhere near an earthed radiator or anything like that, one can safely touch a live terminal and feel nothing.  BUT unless you are in the centre of the room and standing on an upturned  plastic bucket or something you do not know for sure if there is an earthed object nearby or under the floor that totally changes all that and makes the capacitance so much greater as to be a serious hazard.
    But in leather soled shoes or indeed any footwear that is a bit damp, especially on a concrete floor without DPC, or on the ground outside, the effect is mostly conduction, and as many will attest jolly painful ....
    The worst shocks are with two clear metallic contact,  usually one live and one earth or neutral. (occasionally the other phase)  Then there is a defined current path, burns and all the usual physiological effects, and in  extreme cases, death.
  • I still wonder about the actual science behind perceived electric shocks,at college(in Stevenage) we was told its the resistance between you and the mass of earth , but in my thick rubber sole boots on a carpet on a wooden floor this can’t be true.
    Yes, that's the case in that situation perhaps no more than a perceptive shock ... but it's not the only possible fault-current path. Others may include, for example:
    • Hand to hand
    • hand to seat
    • hand to knee
    And it's not just the carpeted floor you may be standing, sitting or kneeling on, but anything connected with the MET (be that appliances, central heating system etc, metallic water and gas pipes, etc.) or Earth (in the event there are extraneous-conductive-parts not connected to MET because they are outdoors.
    'Hand to seat' might appear funny, but I did once see someone get a (perceptive, at the very least) shock between the derrière as it were, to a hand on a tap, from a faulty Class I appliance with a poor connection on the cpc (corroded plug earth pin, damp kitchen, socket-outlet behind the appliance).
  • Thanks for the  answers, I have wondered this for years and even did some experiments with 250V dc,neon screwdriver and met and finally my hand.this proved to me that  it probably not resistive. My niceic area assessor did not know either.