2 x 5kVA 230/110V single phase AC transformers connected in series ( cascaded), would the inrush current (5X) be double or just the same as one? or somewhere inbetween.

I have asked this in some other forums but did not get a conclucive answer.

Its for the protection, there would be no load at switch on, curretly the designers has used a 25A BS88 fuse . from what I have discussed with others,  the inrush current would be the same but for a longer duration as there is no electrical coupling between the two transformers. i.e. the second cannot magnitize until the first has saturated.