EIC or MWC
Scenario:
Existing lighting circuits with fluorescent luminaires upgraded to LED equivalents.
Circuit breaker changing type and/or rating.
Contractor has provided an MWC covering the works.
All looks good, but because the circuit protective device is not strictly a like for like change, should they have actually provided an EIC?
  • Didn't one of the CPS (Napit perhaps?) come up with a cert that could be used as either an MWC or for a new circuit?
  • An MEIWC is just an EIC with fewer details listed.
    What is the point of 'coming up with' something with not quite so many details not listed?
    Should we have an infinite number of certificates for all possibilities?
  • What is the point of 'coming up with' something with not quite so many details not listed?
    Well BS 7617 does permit a near infinite number of possible certificate templates (even the model EIC sometimes needs extending) - but if you have a substantial number of similar situations that are significantly different from the pre-made model certificates, I think it can makes sense to come up with a model that suits you.
  • Yes, when it happens, you can print your own.
  • The point of the customized form is that it is supposed to match what the customer  (more likely their insurance) wants - and if it isn't then the first part of the job of finding out, - what the consultants call 'requirement capture' (and charge for) has failed.
    Some customers, even quite big ones can't handle anything much  more than ' Your wiring is ready and safe to use, and someone else is happy to be responsible for anything being wrong it.'
    Others, not that many to be fair, have more active staff who compare the ZdB with last time and ask if the fact it has changed means something needs keeping an eye on.,,, but that is unusual, far more will not know what to do with the results sheet, and won't have any previous ones.
    It may be that someone used to customer type 1  has now met someone for whom the light touch paperwork is not enough - it all depends what was agreed.
  • I recently attended an educational webinar entitled “Top Tips for Completing Certificates and Reports,” which is part of The Wire series hosted by the NICEIC. The session provided a comprehensive overview of the appropriate utilization of electrical installation and minor works certificates. The content was delivered with remarkable clarity, offering valuable insights into the specific circumstances under which each type of certificate should be used.
  • Hi AMK
    Thank you for providing the NIC EIC guide
    My interpretation of NIC EIC acceptable use of the MEIWC is
    Additional lighting point luminaire
    MAY be used
    The MEIWC may be used
    IF
    Existing circuit protection is suitable
    Which in my opinion referring to the original post it is not as they changed
    Thus as I stated early on in this thread I personally would say EIC was needed and should of been issued.  I wonder if the contractor in this discussion is NAPIT or NICEIC?  Maybe they are neither?
  • What am I missing?  It is the work that is minor or not; not the certificate.
    If you think an EIC should have been used - because the work was not minor and therefore the MEIWC does not include all the necessary relevant details - then you would have used it.
  • All looks good, but because the circuit protective device is not strictly a like for like change, should they have actually provided an EIC?
  • The most important thing is knowing that they connected it up correctly - an alternate choice of paperwork will save no-one from that sort ot error, and worrying about it is a distraction from the proper task of understanding what was actually done.
    M.