Obligation to subject the installation to a battery of tests.

Obligation to subject the installation to a battery of tests.

I was asked to look at an installation of a family friend, who wanted lighting pendants replaced with led tubes. 

The property is occupied by a single old man.

Visual inspection revealed the board was bs3036, no sign of overloading, no thermal damage on the fuses. 

It's a TT system. Bonding for gas and water present. 

Did some tests earthing ze is 106 ohms, ze with parallel paths is 26 ohms and Ipfc is less than 1ka.

Main RCD device is installed upstream but exceeds the time stipulation. At 5x about 236ms.

Did not do an insulation resistance testing or zs of the circuits. 

I'M in a quandary, the chap does not have the finances to upgrade the CU or have new wiring, it's at least 40 years old. 

What should I do?

Do I install a new RCD switch as this will increase safety? If so, am I compelled to subject it to a battery of tests and issue a minor electrical works certificate?

Do I install the led lights, plastic structure class 2? 

I am afraid, if it touches the installation, I may be compelled to do expensive work and no payment.

Do I walk away and not do anything?












  • I think that you have to do what is reasonable.

    I would say that you test upstream of the replacement RCD, but are not obliged to test downstream.

    If you were to test the lot, even at mate's rates for a family friend, you really could open a can of worms. The property could potentially become uninhabitable.

    The MEIWC does not exactly help - see the paragraph at the top of page 514 of the BBB.

  • RCD functional test, trip time at rated current, polarity check, loop impedance, fault currents, bonding etc all  recorded on a minor electrical installation works certificate with a full description of what the certificate covers only (Replacement of RCD). 

  • I was asked to look at an installation of a family friend, who wanted lighting pendants replaced with led tubes.

    What does, "look at" mean please? Perform an EICR?

    If it was simply, can you install a new lamp fitting please, I think that you have been meticulous. Your average reasonably skilful householder would do the task without giving a moment's thought about the rest of the installation.

    I think that knowing what you do now, you have to fix the RCD before doing any further work.

    If you are going to issue an MEIWC, it seems difficult to avoid doing an IR test on the circuit, but I wouldn't risk a whole board check!

  • I would welcome your views as to what are the necessary checks for the RCD change. I hope its Not that battery of all the tests that you would do for a consumer unit change? Ze is done, Ipfc is good, bonding visually checked, will do a R2 wander lead. Any others for the RCD change?? With the light change R2 and IR on the lighting circuits if I proceed with the changes???

  • If you can replace the RCD and leave the fuses as they are, do so, and  ideally do a wander lead earth test (R2 check) and then swap the light fittings,

    I'd suggest if you do any IR test at all, you only do it on the lighting circuits or at reduced voltage L+N to E  as finding and removing all the legitimate loads between L and N is a mugs game and there is a risk of damaging something that got left plugged in by mistake,

    Mike

  • If you suspect that the Residual Current Device is faulty and have conducted the necessary tests in accordance with Guidance Note 3, I recommend providing a quote for replacing the RCD before proceeding with any additional work

  • Sorry. It is separate to the cu. In its own enclosure but meant to say that RCD test was on its load side and not via a socket.  .

  • I assumed the RCD was remote to the board ? So you can’t just replace the RCD ? You would have to replace the consumer unit ? 

  • There is CPC in all the lighting circuits.

    The RCD is a 30ma and tested at the board.

    Do I subject the installation to an IR test. My anxiety is that if it fails the minimum 1Mohms, it becomes problematic. Do I let sleeping doga lay or open the pandora box? 

  • Main RCD device is installed upstream but exceeds the time stipulation. At 5x about 236ms.

    Is it a 30mA device? and was it tested with everything downstream switched off?

    I don't see any immediate need for a new CU - BS 3036 fuses are usually still compliant with BS 7671 requirements. Even if you decide to add SPDs and/or upgrade the RCCB, that can be done alongside the existing CU as long as space and aesthetics permit.