Construction sites and the use of RLV, guidance on the use of residual protection?
 RCDs on 110v sockets
from the discussion above, which is a few years ago, a conclusion was made that RCD’s are not required for RLV/ CTE transformer used in construction sites from Sec 4.
It is clear from section 4 that additional protection for RLV sockets is not a requirement, for obvious reasons CTE 55v etc.
however I have noticed a more recent trend of RCCB’s integral to the secondary side of the windings being implemented to ensure fault protection that can clear within the 5 second disconnection time under 411.8.3. It would seem primarily this is due to chaining multiple extension leads together or excessive lighting circuit lengths, which are difficult to account for except by direct supervision on site.
Blakley, being one of the leading manufacturers offer a great deal of good technical guidance on the subject - but largely it would appear the practice of having both RLV + residual protection combined into one transformer is down to preference rather than a requirement of BS7671 or BS7375 for that matter, meaning this would be ‘best practice’ as apposed to mandatory unless a contractor were to make part of their policy.
I would be interested in the forums opinions on this subject, and your own experiences, I think there are changing trends in the industry as to what was historically an acceptable risk may no longer be the case, particularly I’ve noticed 110v Tx plugged into blue commando sockets with a 30mA RCD protecting the primary side, I’m unsure what degree of protection this will offer to outgoing artic flex on the secondary side and it doesn’t seem it would be the same as a multiple pole device that’s installed on the secondary side?
  • Exactly P-E, practices such as plugging splitter boxes in 32A outlets and then splitting many 16A leads from it or worse still site electricians swapping lighting MCB,s out for 63A breaker when they cannot stop the manufacturer MCB from tripping when long lengths of LEDs are installed and switched on, this is why the circuits will not trip on earth fault.
    grouped residual protection on the secondary side means fault protection will be assured- regardless of external influence
  • As mentioned above, it’s primarily fire risk due to the reasons I also referred to above, there must be something in it or else what would be driving customer demand- some larger contractors have introduced integrated RCCB protection for transformers as mandatory for all projects
  • when it comes to ensuring compliance with the maximum permitted Zs values, especially in scenarios where cable lengths are unknown or the stability of the earthing system is uncertain, we must be proactive.
  • particularly I’ve noticed 110v Tx plugged into blue commando sockets with a 30mA RCD protecting the primary side, I’m unsure what degree of protection this will offer to outgoing artic flex on the secondary side and it doesn’t seem it would be the same as a multiple pole device that’s installed on the secondary side?
    It will have no effect on the secondary side for a fault to Earth on the secondary.
    For an RCD to be used for ADS on the secondary of the transformer in the RLV system, it needs to be located on the secondary.
  • grouped residual protection on the secondary side means fault protection will be assured- regardless of external influence
    Not against L-L faults - which is the only fault you can get on festoon lighting.
  • Yes, which highlights another practice of using modular RCD’s or MCCB’s with earth leakage at the mains distribution which gives a false impression that all equipment downstream is protected to a degree when the reality is only the outgoing sub-mains are protected - not the equipment such as transformers within the install
  • Are you sure, I thought they are 3 core, I’ve not seen anything that says there class II
  • This type are class I
  • or MCCB’s at the mains distribution which gives a false impression that all equipment downstream is protected to a degree when the reality is only the outgoing sub-mains are protected
    Surely if an RCBO or MCCB is used and that meets the disconnection time requirements for the secondary RLVS, that is OK? RCD protection is not necessary on RLVS.
    Traditional festoon lights (in the old days used with insulation piercing lampholders) was certainly two-core - no point in having a c.p.c. since there were no exposed-conductive-parts to connect to.