Ze of PCE (Code of practice for EESS)
I've upgraded the EESS at my off-grid property (new batteries, new inverter/charger/mppt), all up and running as expected and everything working as it should. An EICR is required, and the electrician performing the inspection and testing has raised an interesting point, how to complete the Ze test and what value to put down on the certificate.
The IET Guidance Note 3: Inspection & Testing, when referring to prosumers installations suggest that the Ze test should be taken with the distribution board isolated, and at the output terminals of the PCE (the inverter), but this will just give the impedance of the output stage of the inverter, currently around 5-6ohms. This value being a fail because the supply from the PCE to the distribution board is T-N-S and this requires a lower value.
Again from guidance note 3, from 643.7.3.1 note 1, B, point 2:
“For island mode: if applicable, verification of earth fault loop impedance is determined using measured (r1+r2) values, plus the manufacturer’s information regarding the value of Ze to be assumed for the EESS or the relevant PCE within it.”
All clear there, except I can't get this value from the manufacturer, I've asked and they've gone silent on me.
It has been suggested by another electrician that I've spoken to (who admits to not having extensive EESS experience) that I install another earth rod and make the system TT from the PCE to the distribution board, then anything <200ohms would 'technically' be a pass, but as the PCE and the distribution board are within 1m of each other, this seems a bit of a fudge when T-N-S is preferred according to the latest Code of Practice for EESS (an excellent publication btw, my copy arrived yesterday)...
Something interesting to discuss, how we move forward from here?
  • Hi Graham, yes I was referring to protection against shock by ADS. And the value of the electrode resistance should be low enough to cause the protective device on the output of the Genny to operate within 0.1-5 seconds. In most circumstances an RCD should be used to protect the distribution cable.
  • TN-S arrangement
  • But in a TN-S arrangement, the electrode simply references the N to Earth, it doesn't form part of the earth fault loop. Consider that a DNO's electrode may be between 1 and 20 Ohms, yet Ze for a TN supply is usually < 0.3Ω.
    Faults direct to the general mass of the earth aren't quantifiable, as there will inevitably be a very significant resistance at the point of the fault - as unlike metals soil, even wet soil, has a considerable resistance - so the fault loop could easily be many kΩ so even an RCD can't guarantee immediate disconnection.
  • I am only considering a generator as the primary supply here.
  • Understood - I was just comparing it with a DNO supply, since they're both the same TN arrangement and work in the same way (electrode not part of the earth fault loop).
      -  Andy.
  • Interesting. So is the value of resistance of the electrode not to be considered in a typical earthed generator configuration ? I was under the impression that the value should be low enough to allow ADS in the event of insulation damage on the distribution cable to true earth (Ground)
  • Faults direct to the general mass of the earth aren't quantifiable, as there will inevitably be a very significant resistance at the point of the fault - as unlike metals soil, even wet soil, has a considerable resistance - so the fault loop could easily be many kΩ so even an RCD can't guarantee immediate disconnection.
    I was imagining a mobile generator on standard rubber tyres (like a car). If you touched a live conductor when standing beside the generator, you would not get a shock because there is no circuit.
    However, the situation becomes different if the generator (along with the chassis, etc.) is earthed. So why do we earth a generator please?
  • So is the value of resistance of the electrode not to be considered in a typical earthed generator configuration ?
    Yes, it's to be considered - as I recall BS 7430 recommends max 20Ω (although many seem to be on the opinion that significantly higher values can be satisfactory in some circumstances) - what I'm saying that's got little to do with Zs or normal ADS though in a TN system.
    The problem with faults to true Earth is the resistance of the fault - i.e. the resistance of the soil that's in contact with the exposed live conductor - we just don't know what it's likely to be - it's likely to be many kΩ - so even if you could calculate something, the numbers are unlikely to work even for RCDs. That's why buried cables with any chance of damage need to have a concentric c.p.c. (e.g. armour).
  • I was imagining a mobile generator on standard rubber tyres (like a car). If you touched a live conductor when standing beside the generator, you would not get a shock because there is no circuit.
    Yup - protection by separation. Often used with small generators (e.g. ≤ 3kVA) especially when feeding a small system with a limited number of Class I items.
    Separation is only good for small systems - larger systems have a couple of disadvantages for a separated system. Firstly long cable runs can mean the system goes get referenced to Earth - via stray capacitance (or even imperfect insulation) to Earth (BS 7671 set a limit of 500m of cable in total, and 100,000 Vm) . Secondly while separated system are only OK on 1st fault - as there's no disconnection on 1st fault, a 2nd fault can then occur which can be fatal - and larger systems will typically have more faults than smaller ones (all else being equal). There's also an EMC issue that some equipment with filters etc, like the PE to be connected to the same system as the live conductors, so they can actually divert the unwanted signals somewhere.
    So all in all, larger systems tend to go down the TN route instead.
  • Thanks Andy. How about let’s say HO7RNF generator tails on the surface. What happens if they get cut and exposed copper touches the ground?