Substation Entry- Short section of cable in duct
Hi I am in the middle of a design for a new substation and one of the supplies is circa 150m long and will run for 146m on a ladder in free air. The final 4m will be routed underground into the substation through a duct then the substation trench into the LV switchboard.
when calculating for this if I say the cable is just on the ladder then I need a single 240mm2 cable, however if I say it’s buried in ducts then the cable requirement becomes 3 x 300mm2 cables in parallel which seems extreme in practical sense.
does anyone have any thoughts on this or experience of a similar situation and how to comply with BS7671 whilst still being practical.
  • In some case maybe, but I'm not sure how you would change just the bit in the duct from the middle, or even the end, of a long length, unless at the time you laid the duct in you installed the space to have some joints. If you were planning  that far ahead, you may as well have changed cable size at that point too. Lifespan vs temperature is a very non-linear thing, or more accurately lifespans extrapolated from accelerated aging trials are - in reality we have not even had PVC installed long enough for cold running samples of it to have reached end of life. What we know is that once we get away from the running hot and steadily degrading state, other failure mechanisms that dont show in the accelerated testing can catch you. (estimate the mean time to JCB strike anyone ?)  Or after some decades. other factors now mean the cable is in the wrong place or the wrong size.
  • Very interesting.  Can i ask where the reference for the conduction being in the region of 10s cable diameters has come from?  Would be keen to read more about this.
    Thanks,
    Chris
  • it is just a consequence of  the conductivity of copper (or aluminium) and the length of cross section to diameter. there is almost a one to one mapping between thermal behaviour and electrical resistance, in that the temperature drop is proportional to path length and inverse proportion to area. Note by the way this way of thinking this does not work for things that can convect ;-)
    Basically solve for the easy case of a well-lagged half wire of your chosen diameter, and look at the thermal gradient either side of the lagged/unlagged transition . as you might hope, far from the junction the temperature is at the steady state value for the infinite lagged or finite unlagged case respectively.
    Near the boundary, there is a cross-over where the amount of energy escaping down the wire to escape  from the hot side to the cool side depresses the temperature in the well insulated side and raises it on the cooler side. Temperature is not discontinuous.
    basically to solve, you just need the temperature rise per watt per metre of dissipation in your 2 states, and the conductivity.
    Miike