AFDD protection to comms cabinet in HRRB
Is AFDD protection required to BS EN 60309 socket circuit serving landlords CNS comms cabinet in HRRB? The building is multi residential with commercial amenities. If so does BS 7671 permit similar approach for RCD to omit on grounds of nuisance tripping?
  • Certainly open to interpretation. In these times where some entire installations could consist of flexes plugged together on site (whether BS 7909 style or otherwise) or being located in transportable assemblies, the very concept of "fixed wiring" has probably had its time.
    Also, construction sites, exhibitions, shows & stands (not covered by BS 7909), etc. ... there are other examples out there.
  • Mike,
    In my original post "CNS" stands for converged network services which is essentially structured wiring system with dedicated switches and routers for use of various IP network systems such as data/voice, BMS, electronic security, lighting control etc. Having thought about this some more I think best approach is risk assessment omit RCD and retain AFDD on 32A SPN commando socket on basis that AFDD nuisance tripping is not likely.
  • If it is for CNS then it would be prudent to install a UPS (Uninterruptible Power Supply) especially as the NG (National Grid) has come close in recent months to brown outs
  • Sergio,
    Agreed. Local UPS will be provided within the cabinets.
  • would be prudent to install a UPS (Uninterruptible Power Supply)
    Not a bad idea, but it does have limitations - typically a UPS will only support things for a few hours at most . If the installation is unattended then the nett effect of the UPS on a protective device trip could be no more helpful than to delay loss of service for a short time. That could be mitigated if there was some remote monitoring and people on call 24x7 to attend - but that sort of thing can be costly too.
  • Fire safety or nuisance tripping - which is more important?
    You could wire it straight into the incoming meter tails, avoiding all those pesky breakers.  If the comms cabinet catches fire and burns the whole building down, at least you will know that it didn't nuisance trip.
    That depends on what the equipment being powered is doing.
    What if part of multi-occupancy premises has, say medical locations ?  (Or the question might be asked of AFDD vs no AFDD for 'care homes' ... buy which I really mean 'nursing homes' and similar, but the question could be asked.) In which cases, Regulation 710.421.1.7 clearly provides the answer on the use of AFDDs for medical locations of Group 1 and Group 2, and requires a risk assessment for their use in medical locations of Group 0.
  • Hi Graham. In response to your statement that addresses the application of Arc Fault Detection Devices in medical locations  classified as Group 1 & 2
    BS 7671 indicated that AFDDs are not utilised in these locations. My inquiry pertains to whether this implies that the deployment of AFDDs in hospitals may be prone to nuisance tripping, and therefore, unlikely to provide substantial benefits in such settings ? Im focused on whether AFDDs are recognised for their propensity to nuisance trip. So I suppose, I seek to understand the rationale behind the absence of AFDD installation in medical locations classified as Group 1 & 2. Thanks
    Andrew
  • BS 7671 indicated that AFDDs are not utilised in these locations. My inquiry pertains to whether this implies that the deployment of AFDDs in hospitals may be prone to nuisance tripping, and therefore, unlikely to provide substantial benefits in such settings ?
    There are a number of factors in play, as to why AFDD are not specified for medical locations. The fact that some medical electrical equipment may not fit the EMC signature is only one of them ... another is the fact that if you have a medical IT system, for example, a single fault should not remove power by operating a protective device, just like RCDs.
    I have had discussions with people in the industry, to the effect that they believe some equipment that is not 'domestic and similar' (particularly for EMC environment) may cause unwanted operation of AFDDs, that I understand are constructed for 'Domestic and light industry' EMC environment.
    All I have at the moment is third-party reports of this, without detailed evidence ... and I do not know if some AFDDs are more of a concern than others.