Wiring Matters Mythbuster articles.
Many thanks for the Mythbuster Articles. In Mythbuster #6 there is the following statement
" In itself, this is not a problem, as there is no risk of shock, but a second fault on another item of equipment or a distribution cable could present a shoc
See https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/#:~:text=All%20generators%20need%20to%20be%20earthed%20unless%20floating for Mythbusters #6
Please can you explain further, as my understanding is that if the two class 1 pieces of equipment have their exposed metal parts connected together via the earthing system then I cannot see how a shock risk would occur. If the fault to earth was L1 on both of them then not an issue as such, if one was L1  & one was L2 then fult current would flow and cause the fuse or MCB to trip.
  • What would you recommend people get installed to reduce the risk of electric shock and possible death. I now live in Australia and have looked at AS3000 for guidance and not found anything relevant yet.
    The only 100 % safe option if you don't have an earthing system is electrical separation for each item of equipment, and no provision for socket-outlets at LV.
    The only other workable solution might be the one shown in Figure 4 of James Eade's article, i.e. an unearthed system, with a generator (or inverter) with a line conductor connected to the PE, BUT that system would have to have RCD immediately at the output of the source, as well as one for each circuit. However, this type of system is currently not specified in any of national (e.g. BS 7671, AS/NZS 3000) or international (IEC 60364 series) wiring codes, so I don't think you will get anyone recommending it for a caravan used and under the superintendence of 'ordinary persons' at the moment.
  • However, this type of system is currently not specified in any of national (e.g. BS 7671, AS/NZS 3000) or international (IEC 60364 series) wiring codes
    BS 7671 does seem to mention that sort of system in section 717 (Mobile & Transportable units) - e.g. in Fig 717.1 (if choosing the "without" earth electrode option) and A722 even seems to suggest such a system for EVSE.
    Bearing  in mind that the vast majority of caravans fed by small portable generators and inverters have not got any effective electric shock protection in the event of the faults discussed.
    Don't throw the baby out with the bathwater! Where the system is entirely contained within the caravan (I suspect likely to be the case with battery/inverter systems at least) - then the chances of a fatal shock are pretty minimal (there only being a short relatively low impedance between any two exposed-conductive-parts and very limited fault currents). With a conventional generator stood on the ground outside, or the supply being taken outside, there is a very small risk of a live conductor coming into contact with the general mass of the Earth - typically those conductors would already be insulated & sheathed - which is good enough to class as double or reinforced insulation in most circumstances. And the chances of a 2nd fault is already small - in normal systems we don't usually worry about a 2nd fault on ADS if the first fault is a break in the c.p.c. or a sticky RCD or double insulated systems getting damaged through to the conductors. In many of those circumstances the risks are on par with picking up a badly damaged flex with both hands with one hand touching a section of bare L and the other a section of bare N - and we have practically no defence against that sort of thing in any system.
  • Hi Andy,
    Thanks for your reply I do tend to agree looking from an ALARP prospective that there is a low probability of receiving a fatal shock
    Ian
  • Hi Mark thanks for your reply
  • BS 7671 does seem to mention that sort of system in section 717 (Mobile & Transportable units) - e.g. in Fig 717.1 (if choosing the "without" earth electrode option)
    But not for caravans ... as I said, supervision or training to prevent the danger presented by running a lead outside the unit is extremely important.
    One piece of equipment (vehicle) from one separated supply ... Regulation 722.413.1.2.
    I would add, further, that what is presented in Figure A722 of BS 7671 is subtly different than pure separation, because of the connection of the "PC" (protective conductor) to a line conductor on the separated side. This would certainly be quite serious if it were not for the RCD immediately after the "N-PC" connection. This arrangement is like the 'Floating Generator' of Figure 4 of the referenced IET article, rather than 'electrical separation' as per Figure 5 of the article, the latter of which can only be used under supervision per Section 418 of BS 7671.
    But the very real danger of someone running a lead out of the caravan if socket-outlets are provided is a wholly different matter, and not one that BS 7671 would readily align with at this juncture.
  • Thanks for your reply I do tend to agree looking from an ALARP prospective that there is a low probability of receiving a fatal shock
    I don't think ALARP is applicable here, simply because we have a standard (BS 7671) that says separated systems should only be used for the supply of one piece of equipment only  unless under supervision (which is not the case for most users of caravans)? See difference between 413 (especially Regulation 413.1.2) vs Section 418 (Regulation Group 418.3).
    Or, put another way, 'ALARP' doesn't mean 'within the bounds of what I think I want to do or provide, this is the best I can do' ... the words 'reasonably practicable' in 'ALARP' include taking into account standards and best practice.