I thought this was an interesting consideration from NICEIC Q and A on AFDDs. I would have thought the regulation was focused at what might end up connected to a socket rather than the AFDD protection for the circuit. Were that to be the case, then what about all the other circuits that do not have sockets?
  • 40 years ago, if you were ill, you tended simply to accept doctor's advice. Nowadays, the decision has to be fully informed or else any odd side effect such as gambling all your savings away, or going a bit kinky as in this week's news is the doctor's fault.
    I see no reason why the same principles should not apply to any expert's advice.
    This year, my house insurers required me to install better fire detectors. AFDDs were not required, so that must give an indication as to their value.
  • Wouldn’t it make sense to offer two pricing options—one with AFDDs and one without? That way, the client can decide based on their budget and priorities. While AFDDs aren’t a strict requirement...
    In the OP's situation of HRRBs, HMOs, etc, the wording of 421.1.7 is "shall" - which seems like an absolute requirement to me.
    Earthing and bonding must be adequate for the addition or alteration: 132:16.
    Indeed, but I'd suggest that's not an exception to the rule, but rather it's merely reinforcing the general requirements of 132.16 "No addition or alteration ... shall be made to and existing installation unless it has been ascertained that the rating and condition of any existing equipment ... will be adequate for the altered circumstances".  To my mind that's saying that if we need the supply circuit to have upstream AFDD protection and it's not there, we can't make the addition. Which leaves us with the alternatives of either creating a new circuit with AFDD protection to supply our new socket, or upgrade the exiting circuit so it does.
    After all we wouldn't accept high Zs or excessive v.d. on a new socket, just on the ground that it's caused by the existing installation.
    (I can appreciate that some of the doubt around the effectiveness of AFDDs may give rise to a temptation to look for ways of omitting them, but that can't really justify undermining the principles of the regs.)
  • Hi Andy. I agree that the new circuit should include AFDDs in the specified installations. However, the work being carried out would fall under Regulation 644.1 as a minor works. Does this imply that omitting AFDDs would fail to comply with Regulation 644.1.2
    -Andrew
  • This Technical Bulitin by BEAMA might be worth a red.
    www.beama.org.uk/.../technical-bulletin---afdds-performance-with-xlpe-cable.html
  • Thanks for that - this is the sort of research that should have been published about ten years ago, but better late than never (!) It is not coming to the same conclusions as other authors, but the test conditins appear to be far more 'real world' than some of the lab data.
    I'll have to digest.
    M.
  • Would have been good to have circuits tested at a more representative 10 to 13A for loads imposed on standard socket circuits rather than 20 and 32 A. New purpose built student accommodation in Belfast is wired in a fashion that will never see such current on socket circuits. Care homes might have a tad more current on the kitchen circuits but definitely not on the individual rooms. HRRBs and HMOs the same.
    If AFDDs are only intended to protect fixed circuits serving only socket outlets, then any perusal of fire statistics will drastically reduce the number of fires that are quoted as having an electrical source.
    So to compile a cost benefit analysis, we would need to ascertain the number of fires that had an ignition source caused by arcing in circuits with socket outlets rated up to 32A. Fire statistics are not that granular but I would hazard a guess that there wouldn't be that many!
  • Does this imply that omitting AFDDs would fail to comply with Regulation 644.1.2
    It certainly reads that way to me (for HRRBs, HMOs etc, not as a general case).
  • Interesting article. I noted "The test was carried out by energising the circuit, and manipulating the cable conductor break by a few millimetres, to repeatedly make and break electrical connection and cause electrical arcing." - which made me wonder now long a damaged FIXED cable was likely to continue arcing? or whether, if arcing started at all, it would either erode to an non-arcing gap or weld closed again, in fairly short time. If indeed we're expecting the fixed wiring rather than downstream appliances and/or their flexes to be protected.
  • yes - repeated movement to get it to reconnect is more the sort of thing thing that happens with extension leads. But it is still a lot more realistic  that pre-burning  the insulation with a high voltage that is in the spec. Another realistic sizzle fault not covered is when things are damp or wet, either with pure water or things like mouse urine, the latter of which I appreciate makes for an awkward test.
    It also suggests that the firing within half a second only occurs after the optimum arc has been struck. But this is a different discussion,  one about how useful AFDDs really are with real faults scenarios in practice, not this one, which is more about what the regs think their purpose is.
  • Maybe as a side bar but I think a lot of people are unaware that there are several BS for UK cables.  The type of cable and the type of insulation can make a big difference when people are testing AFDDs.
    BS6004 for PVC insulated and sheathed cables, BS 7211 for thermosetting insulated cables with low smoke and corrosive gas emission, and BS 5467 for thermosetting insulated armoured cables.
    Germany introduced mandatory use of Arc Fault Detection Devices (AFDDs) in its national standard DIN VDE 0100-420:2016-02+Amendment A1, effective from December 18, 2017.
    Now for the bold.  Search when Germany said that AFDD's did not need to be mandated?  What do the German engineers know that we have yet to experience in the UK?