Exporting PME to Socket in high street.
Hi All
First time question,
On doing a EICR on a feeder pillar, in a shopping pedestrian high street. Which controls decorative floor recessed lighting and also Ceeform Socket in manholes in the floor. They access sockets by lifting the lid and then plugging into them. They are market traders that use the outlets and plug in various items small and large Class 1, one of the largest items I have seen plugged in is a Stainless steel Fish counter on wheels, Bake potato ovens on steel benches ect.
The earthing arragement is TNC-s. The panel was contructed by a well know high street furniture panel maker. Wiring may have been done by others. This is a unkown.
All lighting are on MCBs
All sockets on RCBOs
So I have failed/or going to fail the installation due to exporting the PME to the socket outlets and for others reasons.The reason for this was,upon reading the (Guide-to-highway-electrical-street-furniture section 6). As section 6.5 mention being supplied from a TT system. Also in section 6.11.2. On completion of the construction phase of an installation a full electrical inspection and test must be carried out to confirm that the installation complies with BS 7671 in its entirety but especially to Part 7, Section 708 – Electrical installations in caravan/ camping parks and similar locations as applicable.(aiming this should be TT)
Just for clarifiction, am I missing something.As I could not see the manufacture doing this! If they did do it or I'm missing something.
If this is true and should have been TT, then raising another issue if changed there could be  2 earth arrangments within arms reach within the High street.Thats for another day.
Look foward to your Input.
Cheers
Mark
  • HI
    Thanks for your reply
    The client will achive neither of thoses requirements, So this system is going to fail.I still need a work round to satisfy me. I have used this section on another high street, that they look after which operates music stands and other electrical equipment. Again same issues in high street  PME influence everywhere. Or do I look at O-pen as a real option or Electrode at the feeder pillar at 20 ohms.Failing that, it will be TT. but a huge design plan on the possiblities of 2 earth arrangment with in high street. This would than have to be passed to a specialist in this field.
  • Been stuck with this issue going round my head for a good few weeks now with little advicee on how to tackle it or make it safer. Did think about a O-Pen device, but got hung up on the 50v touch voltage for some reason.The Guide to highway Electrical street furniture section 4.2.1 (mentions about a earth rod at max 20 ohms, to limit the touch voltage to 100v on the lighing coloumbs . The O-open device will operate at 70V.
    So my thought is now,Still using the single phase TNC-s system. (As the design planning of the electrical system will be immense, impractical and the cost avoidance required)
    Fit a earth electrode at the pillar to 20ohms (follow the lighing section, this 20ohm electrode is also used for other situations within guidance note 8)
    Fit a O-pen on the mains.( which will pose it own problems retro fitting into a existing system)
    Or let the highways and council sort it out with a electrical designer, which seams the most logical to me.
  • Well in that sense it sounds you could just report back that it fails to meet the  BS7671 derived good practice advice for such situations, and you do not want to recommend a course of action. This is because there is no straightforward and cost-effective  way to improve matters that meets that guidance- which is probably how it ended up in the state  it is now !!
    They either have to re-engineer things significantly, probably at an unjustifiable cost  or accept the small risk of an imperfect installation.
  • Cheers all for the feed back, there are above 15 installations like this. We will get there some how.
  • (mentions about a earth rod at max 20 ohms, to limit the touch voltage to 100v on the lighing coloumbs .
    The touch voltage and the electrode resistance are directly related via the current that flows to Earth via the Electrode. For simple single phase setups, that's only really limited by the load (plus the resistance of the electrode itself of course). For a typical lighting column with a a load <1A,  20Ω would give a touch voltage below 20V which is usually fine. If your sockets are potentially feeding loads of a few tens of amps though, it gets a lot more challenging. A 20Ω electrode only needs 2.5A to flow through it to reach 50V and 5A to hit 100V - and these voltages tend to persist indefinitely as neither overcurrent nor residual devices see anything unusual.
  • BS 7671 does not recognise O-PEN devices for anything other than EV charging equipment installations at the moment.
    There is much debate on whether they would be the right thing for other circumstances, for a number of reasons.
    Section 717 (for mobile and transportable units) and 711 (exhibitions, shows, stands) are probably the closest in Part 7 of BS 7671 to your application, and both do not, in general, permit TN-C-S supplies outdoors.
  • Thank your for reply,
    I have made the cert unsatifactory in both these areas across the diffrent sites.It will require a bit of planning to sort this out. TT it the way forward but as implied from another member the PME influence may be a issue.This is going to be left to a better person than me to sort out. Again thanks for all the responses.You have to love TNC-s..
  • TT it the way forward
    BS 7671 requires that simultaneously accessible exposed-conductive-parts are connected to the same earthing system (Regulation 411.3.1.1).
    TT is not always a conformant solution, in a 'sea of PME'.
    Separate TT earth electrodes, not bonded, is not the "same earthing system".
  • Gkenyon, the mud just got thicker. i will report it back and someone with more knowlage than me can take a look and propose a course of action. There will be be a work round some how.
  • It may be that there is no conformant solution.