Is the UK the only country that continues to permit and deploy TN-C-S earthing systems?
In a discussion about Diverted Neutral Currents, an contributor (Australia I think) suggested that the problem was that it (DNC) is unique to UK.
I'm not that well versed in international systems of earthing, but it's my understanding that while part of the diverted neutral current problem is because of PME (Protective Multiple Earth), and PEN (Protective Earth and Neutral). And that the the problem is likely to be common to all systems, because there is only one planet earth/ground and we all have to be careful with it when latent and patent faults abound.
I suspect part of the issue is that different folks hear different parts of the story and then project the aspect that's different from their system onto the UK system (given we are reporting it).
Is PME / TN-C-S special to UK?
(discussion was in a Youtube video on ' Loose Neutral Fault Explained')
  • This then created the comment that TN-C-S was somehow 'wrong', and my seeking of clarification.
    TN-C-S has its problems.
    But then again, because of protective conductor currents, a broken PE conductor would also be dangerous, potentially lethal, and, unlike broken or high resistance neutrals, you don't get voltage variations.
    TT also has a few potential problems associated with it.
  • however it has a lot of similarity with diverted neutrals
    Definitely one in the same thing really.
  • If all the countries listed have PME like arrangements why is it that from what I have experienced only UK
    One (unsubstantiated) theory might be that the UK's distribution cables are in a worse state than those in many other countries - we perhaps had a widespread network earlier than some, didn't get a massive rebuilding program after WWII, and in recent decades the political arrangements of splitting and commercialising the ownership of the network (where the natural priority became short term rewarding of shareholders rather than keeping the system in long term good condition). Even today a substantial amount of the LV distribution networks rely on old lead & paper underground cables, that only get attended to when they quite literally go bang.
  • Agreed,
    Historically ('50s, UK) home electrics weren't allowed to connect to the Board's [lead sheath] earth and a local earth was required, hence water and gas pipes (highly effective because of surface area (per foot) and length, cf earth rods..)). (source: Father-in-law, often!)
    I guess that at some point the switch was made to PME and that Board's had to provide their earth for cross bonding.
    Meanwhile the Australian commentator is working (possibly exclusively) with twin overhead connections, so see a completely different set of fault styles and quantities. If there is no protective earth conductor then it can't be faulty, bypassed, or be a bypass!
  • in the UK, twin overhead singles are considered an acceptable PME service, since about 1981,  so long as the neutral is double crimped and tied down to gnd with pole base electrodes of 20 ohms or less in total effect spaced at regular intervals. Trees taking out just the lower wire are a rare but not unknown cause of lost neutral.
    Newer overhead stuff going in now is ABC or concentric which sidesteps that issue, but introduces other failure modes.. There is no free lunch.
    I don't think that other countries installations are always much better than the UKs, there are good and bad examples one can find anywhere. Certainly travelling either east or south brings up many examples of 'oh wow'  practice. Even within the same country things can be pretty patchy.
    M.
  • I don't think that other countries installations are always much better than the UKs,
    But of those that use PME or equivalent? (With the possible exception of SA, which if I recall developed their own version of a broken (or perhaps stolen) PEN detector - something like an RCD plus local reference electrode) some time ago).
  • Oh yes. Definitely including  those that use something a bit like PME albeit with legal variations on who was allowed to do the NE bond and where. Most of my personal experience relates to the former East Berlin, but if what the other chaps said about failing aluminium was true, then in some ways that was the good bit of the bloc.. However that has been slowly renovated, so I suspect a  lot of the worst of it has now been redone to VDE whatever number applies or in places like Poland, to their equivalent regs.
    recall this thread, which sadly has lost its scary photos in the software update.
    South Africa is the better engineered part of Africa in many ways and something like PME is one of the many standards.
    If you go the other way, by the time you get to south america, even the 220V parts  like regions of Brazil however, things like basic insulation are missing as well so the fact there is an NE link in a consumer unit is not a total surprise and it really does not matter as the shower is wired in singles  & may not be earthed anyway...
  • Well ... aren't "high resistance neutral" and "lost neutral" quite simply the extreme cases of diverted neutral current (the resistance of the neutral is so high that the alternative path is now preferred by the current, or is the current's only option)?
    Surely some diversion is normal where there is at least one service, gas or water, in metal pipes between neighbours.
    Isn't that why main bonding has to be so substantial?
  • Surely some diversion is normal
    Yes. No-one is disputing that. But if it's "normal" is it "diverted"?
    When we are talking about "diverted neutral current" we usually mean it's not flowing where we expect it, usually in greater magnitude than we expect.
  • New 100A TPN TNCS supply into a city centre restaurant we are doing. Love the plastic bottle supporting the joint.