what JB/enclosure required for fire alarm installation
I am not an expert but re fire alarm systems but I need to split my fire loop due to modular project requires that.
Once the whole project delivered on site everything will be connected back and stays for years.
I have come across conflicting opinions about this.
Some say that this has to be done by using fire resistant plastic JB with ceramic terminals whereas other says that it need to be steel box not plastic.
I have fount both of them plastic and SS JB and they both actually "fire resistant" so I am confused completely.
  • Thanks for your answer Will.
    How do I know in the standard cable terminals I use (Wieland) are rated to the same level as FP200 cable is?
  • To be the same rating as the cable the joint would need to be ceramic I’m not personally familiar with eth Wieland range so if they are plastic then the answer they are not
    Not my area, so just out of curiosity... I can follow that logic for say the old mineral insulated cables (pyro etc.) but FP is basically a plastic insulated cable (with an aluminium screen) - pretty special plastic perhaps, but still plastic. If the terminals housings were made of the same (or better) plastic, wouldn't that do?
  • Fire resistant cable (FP) is tested to annex E of BS EN 50200 this standard includes different classifications based on the cable's ability to maintain circuit integrity under fire conditions, with classifications such as PH15, PH30, PH60, PH90, and PH120 indicating survival times in minutes. Annex E introduces The "CWZ" designation which refers to a specific test sequence within BS EN 50200 that includes a direct flame application, mechanical shock, and, a water spray, to simulate fire and its associated hazards.
    • Flame Test:
    Cables are subjected to a direct flame at a specified temperature (e.g., 830°C).
    • Mechanical Shock:
    A steel bar strikes the cable or its mounting backboard at regular intervals.
    • Water Spray:
    Annex E of BS EN 50200, included in the CWZ test, introduces a water spray component.
    While FP 200 is a soft skin cable it’s not plastic, as it needs to survive 830 degrees C. so the short question is can your connectors survive 830 degrees C? if they are plastic I’m guessing the answer is no.
  • While FP 200 is a soft skin cable it’s not plastic, as it needs to survive 830 degrees C
    What is it then? https://datasheet.prysmian.com/pdf/datasheet/en-GB/312420/GB00_FP200GOLD
  • "Insudite" insulation is the stuff in FP200 and is a high temperature cross-linked polymer. And gets tested at 830C for an hour and then  hit with a baton to make sure the cores do not migrate and touch once hot.
    It would be sensible to make terminal blocks of the same stuff ,but I don't think anyone does.
    Bonkers to think there is a plastic that more or less survives well above the temperature of molten aluminium (~ 660C), but there you are.