Solar PV into load side of RCD
At Section 8.8 in the COP for Grid connected Solar PV systems it clearly indicates that the inverter should not be connected to the load side of any RCD that is shared with other circuits. The note explains the reasons without elaboration.
I am trying to understand how an inverter would continue to supply the fault after the RCD has operated. Is it not a separated circuit at the loss of supply?
  • Thinking even how to detect, let alone any kind of ADS.
    RCD, except in IT or separated systems.
    (In TN and TT systems, N is at 'earthy' potential, so current flows between L and feet as well as L and N ... the RCD might just detect enough residual current and operate in a time that might save you, but there's no guarantee of safety!)
  • so current flows between L and feet as well
    Seems pretty unlikely unless the victim is barefoot on wet ground, or happens to be simultaneously in bare skin contact with an exposed- or extraneous-conductive-part. Body resistance normally limits shock current to a few hundred milliamps, and you'd need a sizeable proportion of that to run to Earth for the RCD to trip - i.e. that path would need a loop impedance not significantly higher than the direct skin contact L-N path - I'd suspect even a pair of sweaty socks would provide enough resistance for 90%+ of the current to stick with the easier L-N route and be missed by the RCD while the victim gasps their last.
    Nothing's perfect of course - there are always risks especially where multiple simultaneous faults are possible. ADS can be defeated entirely by a simple pre-existing c.p.c. break. The long standing general principles only provide shock protection between two or move live parts by insulation, enclosures,etc and good maintenance; not ADS. It doesn't seem fair to make things more onerous for local generation.
  • Body resistance normally limits shock current to a few hundred milliamps,
    10s of mA is enough to kill ... and only 30 mA needed to operate a 30 mA RCD in 0.3 seconds (admittedly, up to 250 mA might be needed to operate in 0.04 seconds if the manufacturer selected that option instead of 5 IΔn for their product as per BS EN 61008-1 or BS EN 61009-1)... as I said, protection not guaranteed, but you still have more chance than no RCD.
  • It doesn't seem fair to make things more onerous for local generation.
    It doesn't seem fair to say that protective devices have to disconnect the source, and then circumventing that with a generating set supplied downstream of a protective device that's intended to provide protection of final circuits.
    Is it actually more onerous, or just common-sense?
  • It doesn't seem fair to say that protective devices have to disconnect the source,
    Not for L-N shocks though.