Special Locations Pool Rebar Bonding

Hi all, in a domestic pool installation, the contractor has formed the concrete base of a swimming pool, linked to the main house, and not bonded the slab rebar. My understanding is that the contractor will now need to expose the rebar and bond back to the main earth terminal. My concern is this will affect the integrity of the pool slab (future weak spots and leaking) and also whilst trying to achieve complete rebar continuity could result in many holes. I believe there is insulation and screed going on top of the slab (I maybe wrong), could a secondary earth nest be sat on top of the slab or would this create more issues by in essence adding secondary extraneous conductive parts?

  • To provide a TT system feels like the correct method as we are then in control of a single earthing system for the entire property, not a hybrid of two earthing systems that are linked (which I'm not sure is compliant)

    The only thing to consider, is if extraneous-conductive-parts of the installation, particularly metallic service pipes, are shared with other installations, or whether those pipes (or earth electrodes) are installed close to metalwork connected to PME below ground. If so, you can't get away from PME.

    Does require some thought before you start work, though, because it's far more difficult when all the work is complete, to try and back-engineer the TT approach (especially if work is needed below ground to check distance of electrodes from other services/metalwork).

  • not a hybrid of two earthing systems that are linked (which I'm not sure is compliant)

    It's common enough in practice ... think of a pair of semi detached houses with bonding to common metallic gas and water supplies.

       - Andy.