Earthing and Bonding Design for 690V AC Railway Tunnels

Dear IET Technical Team,

I am an IET member (MIET) currently reviewing the earthing scheme for about 5 km AC train 960 VAC tunnel supplied from two substations (each with separate earth electrodes, ≤5 Ω). Both substations are interconnected by two paralle

System Configuration Overview:

  • Each substation is equipped with its own earth electrode system designed to achieve a resistance of ≤5 ohms.

  • The substations are electrically interconnected via two parallel protective earthing (PE) conductors that run along the full tunnel length (5 km), ensuring both equipotential bonding and redundancy.

  • These PE conductors are intended to:

    • Interconnect both substation earthing systems,

    • Provide a continuous protective earth along the tunnel for all connected equipment (lighting, SCADA, signaling, etc.),

    • Bond all exposed conductive parts and metallic structures inside the tunnel.

  • I would appreciate the IET’s expert input on the following aspects:

    1. Is the use of only end-point earthing (via the substations) with continuous PE conductors across 3 km acceptable for a 690V AC system, assuming the conductors are adequately sized and bonding is done at regular intervals?

    2. Would additional intermediate earthing electrodes or equipotential bonding bars be recommended, especially to mitigate the effects of fault current return path impedance or potential rise under earth fault conditions?

    3. Are there any best-practice thresholds for voltage drop or rise along PE conductors during fault events in such long LV systems, particularly with respect to maintaining safe touch and step voltages in a tunnel environment?

    4. Which standards would best guide this setup from the UK or international perspective? (e.g., BS 7671 Section 542, EN 50122-1 for railway applications, IET Code of Practice for Earthing, or IEEE Std 80?)

  • —not for direct strike protection inside the tunnel,

    No, but direct strike to the infrastructure outside the tunnel can affect those in the tunnel, and systems (including earthing if you interconnect both sides) that go from outside to inside from either end

  • Yes, that is correct. Accordingly, Surge Protection Devices (SPDs) have been provided at all service entrance points.

  • Good Morning Mansour

    I have no specialist knowledge my self in railway earthing systems, just a passing interest, so I am unable to offer technical advice myself.

    However the IET does publish a very good book on the subject, The Guide to Earthing and Bonding for AC Elecrified Railways. It covers the theory and practice of earthing and bonding of different types electrified railway traction systems. 

    You may find it useful to understand the theory and to supplement your local regulatory requirents.

    I had a long and informative conversation on the subject with one of the contibutors to the Guide at the IET headquarters when he was a member of the IET JPEL 64 committee.

    Hope this helps?

    JP

  • See my post above.

  • Good morning John,

    Thank you for your kind response and for pointing me towards The Guide to Earthing and Bonding for AC Electrified Railways. I appreciate the recommendation, and I will look into obtaining a copy to supplement my understanding alongside our local regulatory requirements.

    It’s also interesting to hear about your discussion with one of the contributors and their involvement in the IET JPEL 64 committee. Such insights always add value to the technical background of a reference.

    Thanks again for taking the time to respond and share this resource.

    Best regards,
    Mansour 

  •  NFPA 130 (2023) CHAPTER 7 Traction Power and 9 Emergency power, grounding and bonding.