There’s debate about exposed basic insulation in meter cupboards being satisfactory or not? Industry guidance (WRAG) say it’s satisfactory if the door’s in good shape, what’s people views on this ?
but it is an issue for premises in which the Electricity at Work Regulations applies ... including, perhaps electrical laboratories and workshops.
What sort of thing did you have in mind? I was thinking that an entire room could meet the definition of a 'dedicated' enclosure if only electrically skilled/instructed people had access ... but allowing the caretaker to store brooms in there for example would mean that other precautions would be needed.
I would further add, that there's nothing to stop any other enclosure using "meter box" or "lamp post key" in any type of installation ... and such keys are readily available.
Indeed - likewise a screwdriver - hence my comment about the intent being less to reliably prevent access, and more about making it obvious that electrical hazards lurk behind. A switchroom with "Electrically authorized personnel only" on it is more obvious than a broom cupboard, even if they both had the same kind of lock on it. Most people would think they should be able to read a meter in a meter box without being exposed to additional risk of shock.
Also, will this be agreed with the DNO beforehand when the SWA cable is directly connected into the REC isolator.
There remains the issue of protecting the circuit from the meter to the consumer unit busbars. Regulations 433.3.1 (iii) and 434.3 (iv) allow the designer to utilise the DNO’s main fuse for this purpose, provided the DNO designer agrees that the characteristics of the device are suitable.
For short-circuit protection a 100 amp BS 88-3 (formerly BS 1361) fuse would provide adequate protection provided the meter tails are a minimum of 25 mm² and no longer than 3 m from cut-out to consumer unit.
Having read all the way through this thread, one most important aspect is missing. Why is this question being asked in the 1st place? Has it been sparked by a sudden increase in fatalities due to faulty or missing meter cupboar doors? How many people have been killed as a direct consequence? And out of those, how many were of the skilled and instructed variety and how many were simply joe public?
Finally, is it worthwhile to contine the debate? In todays world we seem to have become afflicted with an almost addictive need to look for non problems and then over-diagnose them to death when our time could be better spent on other more vital stuff.
Bank holiday rant over! But what do others think about how this affliction to agonize endlessly over nothing in particular and then diagnose and label it as a dangerous negative seems to grow and grow Must be keeping some otherwise unemployable person in a job somewhere.
I think the whole thing is a storm in a teacup.
If someone wants to read the meter, then they will open the meter box and read the meter. At most, they will have to poke a button on the meter to wake up the display.
I can't see any consumer then deciding to do something stupid like attacking the single insulated meter tails with a pair of scissors.
Yes, but others might need 'supervised access' to the room for other reasons. That 'supervision' can be addressed in places where safety management systems are in place, but not in a dwelling ...
As others have said, is there a risk of shock? Electricity meter boxes conforming to the relevant British Standard do have an electricity warning sign moulded into the door, so there is a warning to take care ... and all parts should be covered with at least basic insulation ?
Dumb question: is there a quotable calculation of the impedance of such a cable for ensuring sufficient prospective short circuit current to ensure the fuse blows? - I ask as an 'electronics' engineer and having seen lots of questions about the "why 3m" limit
It's the common sense problem: neither common nor sense [on both sides of the electrocution]
I believe it’s more a rule of thumb precaution due to supply loop impedances as DNOs are under no legal obligation to provide or maintain any particular value of earth loop impedance and during the lifetime of an installation a number of circumstances may alter the earth fault loop impedance.
Yes, in a TN system, if you assume the distributor's cutout can provide ADS (there's no guarantee they will agree to that). Table 41.4 of BS 7671 implies 0.38 ohms for a BS 88-3 fuse (a BS 1361 in some service heads would require around 0.35 Ohms taking into account 230 V and Cmin of 0.95 in case anyone looks back at the loop impedance tables in 16th Ed) ... something that's probably OK in most TN-C-S installations, but not in some TN installations. The use of an SWA cable brings in the need for ADS (normal "tails" don't require ADS as they are considered equivalent to double or reinforced insulation, something SWA in general can't achieve.)
... which causes a problem in a TT system unless you fit an RCBO or RCCB in the meter cupboard.
In fact, a 300 mA RCBO would work for both TN and TT.
However, the 3 m limit is not for protection against electric shock, but protection against overcurrent ... one of the requirements for not having to provide protection against overcurrent in certain circumstances.
Depends what you mean by “meter box”. I doubt anyone would feel comfortable with single insulated cables in this meter location;