Incomer Protection Requirements where LV cable is direct from transformer?
where the LV cable from the transformer is directly terminated at the transformer LV termination box i.e. no circuit protection on the LV take off chamber and feeding into our LV ACB incomer downstream. what is the requirement for circuit protection specification at the LV ACB here? We have been told that the LV earths need to be separate from the HV earth, so we've considered the system to be a TT earth from the LV ACB downstream and will include ground fault settings as an integrated part of the CB specification.
However do we need to consider the cable between transformer and ACB as this would be unprotected and not subject to earth fault as we have no cpc between transformer and ACB panel? is this section of cable subject to any '' IT '' considerations?
quick sketch to try and make clear what i'm on about :)
thanks
  • thanks Andy, yes it does help very much. thank you.
  • Hi Andy,
    It's typical for the LV cable box at the transformer to be a Class 1 enclosure. I'm struggling to see how it'd be possible to adopt the protective measure of double or reinforced insulation.
    Kind regards, Bh.
  • do you mean just metal, like the transformer core and tank, normally HV earthed. Or actually bonded to the secondary neutral ? - its the latter that makes it LV class 1.
    The LV bushings are normally rated to more than basic insulation.