please forgive this daft question, and I accept that I may be reacting to a non-existent problem
if I'm reading the wiring regs correctly, then we can protect the origin of an installation against overcurrent (whether overload or fault) by using the distributor's protective device with their consent. However, I can't see an equivalent provision to protect the origin of an installation against electric shock by similarly using the distributor's protective device for automatic disconnection of supply
I'm thinking of industrial supplies where the meter is in a substation at the edge of the site and the main DB is in a building on the other side of the car park, so the only protection for a couple of hundred yards of incoming cable is whatever the distributor has fitted at the substation