Using mains cable for control wiring, what about colour coding, and then a question about armour
Hello everyone,
Two questions for a personal project:
1.
I'd like to run some extra cable between my house and our heat pump for possible future use for controlling 3-way valves. My understanding is that BS7671 asks for 3-core control wire to have the neutral/mid-wire be blue, and the other two wires to be one of a range, but not yellow/green like an earth wire. Our heat pump asks for these wires to be 0.75mm2 CSA and as they're for mains voltage they'll have a suitable voltage rating too. However, I've searched around and can't find any 3-core cable which complies with all of these requirements.
The main sticking point is the colour-coding. I can only find 3-core cable in either standard mains colour-coding (brown, blue, yellow/green) or in 2x black and 1x yellow/green. I thought of running a cable with many cores, as I need to run a bunch of 2-core as well for other possible future uses, however all the multi-core I can find also follows the black+yellow/green coding. I can't find any suitable 3 or multi-core wire that has any blue cores!
So, I was wondering what's acceptable, or what's the common practice. Just use either the mains or the black+yellow/green multi-core wire and sleeve it to make it clear what's doing what? Or do I not need to do anything at all?
For reference, the existing wiring from the install done a year+ ago uses a black+yellow/green multicore to run out from the wiring centre to the heat pump, and mains-coloured 3-core inside the house from the wiring centre to the connection box with the 3-way DHW valve. This suggests to me that black+yellow/green multicore is acceptable without sleeving, however it's the fact that BS7671 seems to ask for a blue core which has me bamboozled.
2.
As said, the cables need to run out from the house to the heat pump, it's about 7m total with about 1m actually underground. The cables are in trunking the whole way, even when underground. I don't think the existing cabling has armour, so I wasn't going to buy armoured cable for these new runs, but as I was already writing a question I thought I'd ask about this too.
3. ;)
Not a question, but for complete info I also need to run a 5-core cable for connection of the heat pump's wired controller which will follow the same route. It doesn't need 0.75mm2 and doesn't carry mains voltage. The heat pump manufacturer told me that it doesn't need to be screened/shielded and even Cat6 cable would be fine. I was just going to buy a 5-core multicore cable for this.
Cheers Slight smile
  • At this rate he'll be driven to installing singles in flexible conduit instead.
    Now that's an idea...! :D
  •  then why aren't all cables just black multicore with a yellow/green for earth? Yes sleeving is allowed, but it's not preferred if the right colour cores are readily available is it?
    Anyway, in this case I can't find the cable with cores in the right colours, so I'll have to use sleeving anyway.... and to be compliant with both BS 7671 and BS EN 60204-1 I should use blue and red sleeving on the neutral and red and one other colour on the live conductors.... but I think that's probably getting a bit silly.
  • In practice while it would be nice to always follow the letter of the standards, I don't think anyone will mind what colours you use, and the electrons certainly won't.  so long as you don't misuse green and yellow, and whatever is done, please label or  record it somewhere for the next person in, or if your memory is as good as mine, for your future self.
    I think that this is the answer - a wiring diagram with wire colours written on them, together with wiring labels and colour sleeves.
    That is more complicated, but is to do with harmonization originally agreed in the late 1960s by and for international cable manufacturers.
    We're rather late to the party on that one - it happened before I was born !
  • My difficulty was finding 3 core cable suitable for control wiring for a 3-way valve, one neutral and two live conductors, which would comply with BS 7671 where the neutral should be blue and the others permitted to be a range of other colours but not yellow/green.
    SWA would be the usual choice for outdoors/underground.  You could use 3-core, oversleeve black with brown as your 2nd L and grey with blue as N and use the armour as the c.p.c.Or four-core (which has a blue core) and oversleeve for 2nd L and c.p.c. or 5 core which usually gives you a blue and G/Y cores (plus a spare core for future expansion). (The armour still needs earthing at at least one end whatever).
  • Thanks for the suggestion , as sleeving is required anyway it seems that the core colours aren't really important so I might as just buy the most economical cable that meets other specs. I agree that SWA is what's needed for direct burial but in this case the cable runs through a duct for the short section when it's underground so I don't think the SWA is needed.
  • Save that Will D specified 0.75 mm² and I think that the minimum size for SWA IS 1.5 MM², so it would be necessary to ensure that it would fit the terminals.
  • the cable runs through a duct for the short section when it's underground so I don't think the SWA is needed.
    Depends on the specification of the duct (and to some extent the situation) - the basic requirement is for any cable buried in the ground (directly or indirectly) to have an earthed armour or earthed metallic sheath - the idea being that even if it's struck with a digging tool or hit by a driven piece of metal it should remain safe as it would trigger automatic disconnection of supply as soon as the item hits a line conductor (as it would also be in contact with the armour/sheath). A cable without armour but in a duct would have to provide equivalent protection - which in the absence of ADS would usually mean a duct that would mechanically prevent damage to the cable - which to my mind is tricky for a plastic duct when faced with the likes of a pick axe or steel plant stake, or you'd need some other means of showing that such damage wouldn't occur (e.g. it's in a controlled environment where no-one would ever dig without permission and have all the plans to show the location of buried cables etc.). Some guidance is suggesting the the highest grades of plastic ducts may provide adequate protection - which is especially welcome in certain situations where the earthed armour approach doesn't really make sense (e.g. unearthed DC PV cables) - but I think for most, SWA in ducts in still the norm.
  • Anyway, in this case I can't find the cable with cores in the right colours,
    There is a reason for that ... power cables with flexible conductors and up to 5 cores, with core identification by colour, are affected by European harmonisation that goes back to the late 1960s. Other power cables with up to 5 cores will be manufactured to align with the national wiring standard for power circuits (in the EU and UK these align with BS EN IEC 60445, but there are variations of the line conductors, for example UK and Ireland these are BN, BK, GY, but some countries use BN, BK, BK)
  • I will admit that I'm starting to get a bit lost with all the standards, variations, possibilities. However, maybe going back to the root of my original question, which is why the wiring regs say that for control the colour of the neutral or mid-wire must be blue:
    electrical.theiet.org/.../bs-7671-2018-corrigendum-dec-2018-v2.pdf
    I've referenced a free corrigendum because 1) I don't actually have a copy of the wiring regs to reference and 2) the corrigendum is freely available for anyone to access.
    I appreciate that in most 2-wire control cases a simple L+N brown+blue 2-core cable will suffice. In my case I'm looking for a 3-core cable for control of a 3-way valve, which in a domestic setting isn't that unusual for a heating system. If this is a fairly common type of cable-need, then why can't I easily find this kind of cable in the UK? I appreciate that there may be another standard for colour-coding of 3-way valves for heating systems which I'm not aware of (just as I wasn't aware that BS EN 60204-1 would apply to external wiring for a domestic heating pump). However, if I've not missed something, then why can't I find this cable which surely must be needed in lots of situations in the UK? Maybe the answer is just that it's not needed frequently enough to justify the existence of a specific cable.
    Or, maybe 3-way valves were never the intended purpose for the colour-coding for control wiring in the wiring regs? If that's the case, then what does it mean by "mid-wire"?