Gas bond in detached garage ?
Hi Guys.
I carried out an EICR earlier and am a little unsure of the bonding setup.  House built in 1982. Original wiring which is ok. 16mm tails/6mm earth. 6mm bonding conductors. 60 amp main fuse.
The gas meter is in the detached garage. About 2 meters from house. There is a 6mm gas bond in there at the gas meter that is clearly under sized as it has been taken from the 2.5mm supply cable for the garage power.
The gas pipe from the meter goes through a 4inch duct and pops up in the kitchen below the units next to the water pipe. Both are bonded there in 6mm. This area backs onto the garage so in reality 2 or 3 meters away if that is relevant.
My question is is the bond by the gas meter actually required as it is outside anyway or will it potentially need upgrading.
My gut reaction is it is fine as it is. There is no water in the garage.
The supply pipe to the gas meter drops into the concrete floor and as far as I can chip the floor away looks steel, although I am only seeing threading nut connections before it is buried so may well be plastic.
Any guidance would be appreciated
Thanks.  Gary
  • The existing 6mm is fine, as no thermal damage is present. I would go further and use the adiabatic equation to confirm compliance, as mentioned in PME. If the gas pipe comes up at different places, verify if it's extraneous. Same setup: if gas enters a commercial warehouse, it would require a protective conductor. This may go back under and enter at another location within the warehouse, requiring another protective conductor. It's hard to picture the scenario without visuals. Hope you get sorted in the end, pal. As I always say, not one size fits all, and not all one design fits all.
  • the adiabatic equation to confirm compliance
    How would you do that for a PME bonding conductor? Diverted N currents (as they may come from outside of your installation) as basically unknown in magnitude and their duration may be indefinite - so blowing the conventional 5s limit to adiabatic out of the water?